danny124

Hi guys got a right head scratching moment..... Wondered if anyone has come across this situation...

I did a rewire for a property (downstairs only), Started doing the testing, everything was good untill i got to the IR test. No SELV, no bulbs, nothing pluged in etc etc...

Example testing the lighting and getting IR readings of 750-ish, but really in i want >1000Mohms as its all new. other circuits like cooker im getting 820 Mohms.

I disconnected all the lighting and did an IR on every leg and then got a resistance on every one as >1000. reconnected and went back to the 750...

I then did an IR test on another job, and got >1000M ohms straight away.

Has anyone has this problem before, i got a right head scratching moment here....
 
You will very rarely get 1000 meg ohms depends if it is surface chopped in only needs to be a little pressure somewhere in a metal back box or a little tight where the plasterer has fitted his plaster board onto the walls im happy with 200 meg ohm and above i dont think you will get perfect readings not in the real world
 
thanks for your reply guys....

all circuits were tested induviduallay and as a whole, with and with out rcd....

so..Robskiing as if my readings are like that and written on cert it should be ok, no questions asked... I just never seen or had this before....
 
Hi odigi, was testing the lighting (with no transformors connected at that point, no bulbs) and cooker and ring, cooker wasnt connected at that point, and nothing plugged in either.....

Cheers rob, just got my registration, and just being cautious. Maybe being too cautious...
 
Normally when im doing an install at the new board i strip and sleeve the new cables to where they are going and test each circuit individually usually r1 & r2 first then i do my insulation resistance before i connect them this saves a little time nothing is worse than connecting a board up then you have to take them out again to test but everyone has their own way of doing it you will in time find one way that suits you
 
haha, your not on your own, thats what i do... Thats how i came across my problem..


danny 124 You dont have a problem :)
Remember that the insulation resistance test is an"whole of installation test "
Individual readings do not give the correct installation reading
 

Reply to Insulation resistance....Head scratching moment in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
284
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
783
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
804

Similar threads

  • Question
There can be a few reasons for low L+N -> E readings: Connected equipment is leaking. By design, or just old/damp SPD are connected (but there...
Replies
9
Views
2K
  • Question
I may have been mistaken regarding TT I will look into that, thank you for the valued reply, but in general I stick to my post, a good topic for...
2
Replies
24
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top