schoe
Hi all having a few issues with an insulation resistance test on a ring main. Firstly carried out my continuity test,
End to end,
L-l 0.93 n-n 0.90 e-e 1.46
R1+n 0.47 r1+r2 0.61
So then moved onto the insulation test.
Checked all the sockets for tightness, made sure nothing was plugged and disconnected the wires from the consumer unit to test separately.
L- n <500
n-e <500
then l-e 246.
Now I no this is an acceptable reading on the line to earth but the cable is newly installed so don't understand why I'm getting the lower reading.
I've even check each leg of the ring by disconnecting the socket and doing an insulation resistance test in-between each leg. After completing this though every leg passed the 500 mohms. But when I re tested the circuit as a whole I would get the same lower reading again. I really don't understand why, if anyone could offer any advice i would really appreciate it.
Like I said before all the wires were disconnected from the consumer unit and nothing was plugged into any of the sockets.
Oh and I have even put all the ring in choc blocks to make sure the sockets weren't faulty but I still got the same results.
King regards chris
End to end,
L- n <500
n-e <500
then l-e 246.
King regards chris