There are no neons on the switches.

There is a tv amp in the attic, would that be spurred from lighting by any chance?
They often are, try unplugging it and retesting. If it clears then there's your problem, hopefully you won't have fried it. This is an example of why it's wise to do a test on 250v before the proper one at 500, they don't like it up em
 
For all it takes its wise to do a quick continuity test between L & N before applying 500V.

Edit. Or as Trev states IR test at 250V
 
Last edited:
I'm pretty sure it's the tv booster!

Will check it out tomorrow as its a property I have just purchased to rent out. Therefore, no rush whilst its unoccupied.

Cheers for all the advice :)
 
I'm pretty sure it's the tv booster!

Will check it out tomorrow as its a property I have just purchased to rent out. Therefore, no rush whilst its unoccupied.

Cheers for all the advice :)

You may need to buy yourself a new amp

Every day is a learning day - but I really don't know what possesses people to do a 500V IR test on a system which they are not 100% familiar with
 
You may need to buy yourself a new amp

Every day is a learning day - but I really don't know what possesses people to do a 500V IR test on a system which they are not 100% familiar with

I struggle to understand why people have test equipment when they can't understand test results it gives them.
 
Hi all,

Just a quickie. I carried out an insulation resistance test on a lighting circuit which only has two rooms consisting of 4 lights.

Live to earth and neutral to earth was fine but when I tested live to neutral I got a short circuit.

All the bulbs were removed so just wondering if anyone had any ideas?

The Zs reading was 0.73 ohms.

Thanks


It's those daffodils you're using in the lighting circuits mate.
 
if there was a short circuit between a phase conductor and neutral...either a protective device should have tripped or operated ...or you would have had something go...BANG !!!
 

Reply to Insulation Resistance - Live to Neutral short in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
373
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
939
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Thanks, I was hoping someone could confirm whether it was odd or not. I've done a fair bit of insulation testing but only on a small number of...
Replies
4
Views
285
  • Question
I may have been mistaken regarding TT I will look into that, thank you for the valued reply, but in general I stick to my post, a good topic for...
2
Replies
24
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top