Although insulation resistance of 26.9 ohms on a ring circuit and 22.5 ohms on a light circuit are with in limits, these are still low. What is the easiest way of finding and correcting the cause of the low reading?
 
Sorry,but another question

Is this a hypothetical situation or are you thinking of finding and attempting to increase the readings on your installation

The insulation test result should be the whole of the installation with all circuits tested together
The reading should be one reading for all circuits



They are satisfactory readings for an installation
The comparison with readings that may be 200+ cannot be made because each installation has different equipment connected and results vary

Why do you think there is lower than expected readings ?
 
Des, isn't that for new installations where the supply isn't connected yet mostly, correct me if I'm wrong please?

I tend to test the circuits separately and given readings like that you need to take into account the age of the installation, whether theres any sign of vermin infestation or just plain old bad connections.

If its new wire that you've just pulled through then you may well have a problem as it should have exellent readings.
 
Des, isn't that for new installations where the supply isn't connected yet mostly, correct me if I'm wrong please?

The Regulations and guidance refer to testing the installation as a whole, or if this is not practicable then the individual distribution boards as a whole. So I would say no, in general you should avoid insulation resistance testing the circuits individually and do the whole installation in one go where practicable.

Otherwise you will need to consider the effect of the resistances in parallel.
 

Reply to Insulation resistance low in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
706
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
3K

Similar threads

Thanks, I was hoping someone could confirm whether it was odd or not. I've done a fair bit of insulation testing but only on a small number of...
Replies
4
Views
340
what is the piece of equipment and part number?
Replies
9
Views
577

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top