Hi guys, another silly question, how to measure the insulation resistance in a 3phase circuite? shall i do it in 2 steps?

1: between cu and isolator/starter.
2:between isolator/starter and 3ph socket

cheers
 
Turn off power.Simple installations should be checked as a whole.test to earth from all live conductors including neutral connected together.or each live seperatly to earth.when you have vulnerable circuits i.e.. dimmers etc.i think.
 
hi, i am still bit in dark, when i test continuity of a 3 phase circuit i should test seperately between cu and isolator; isolator and socket, then add up, but when testing insulation why should i test it as a whole?

please enlighten me!
 
Hi Bluesky,

You don't want to be doing it circuit by circuit - you'll be there 'til the following day:)

The procedure is simple.

Sub board main-switch open.

Motor isolator open.

Dimmer bypassed.

FCU bypassed.

All other switches closed.

Three phase board - all MCBs closed. Main switch open.

Select 500v range and perform ten point test.

i.e.

Place probe 1 on earth bar and probe 2 onto - L1.....L2.....L3.....N (4 tests)

Place probe 1 on neutral bar and probe 2 onto - L1.....L2.....L3 (3 Tests)

Test L1 - L2, L1 - L3, L2 - L3 (3 Tests)

NOTE: L1, L2 & L3 are tested on installation side of 3-phase main switch.

Then:

Test from motor isolator to motor (or 3 phase socket)

Test single-phase sub-board circuits individually (due to RCD) - should be two circuits - don't forget to throw the two-way switch to test your strappers.

Job Done:)

Don't think I've forgot anything.

PS
The 2391 board will be TN-S, if you had a TN-C-S supply you woulld have to remove the neutral test link otherwise you would get continuity between neutral and earth.
 
Last edited by a moderator:
The 2391 board will be TN-S, if you had a TN-C-S supply you woulld have to remove the neutral test link otherwise you would get continuity between neutral and earth.

You need to break the neutral link on any TN system - TN-S included - for the purposes of an insulation resistance test.
 
You need to break the neutral link on any TN system - TN-S included - for the purposes of an insulation resistance test.

Hi Risteard,

I understand your reasoning, but I didn't on my 2391 and the assessor didn't say anything.

We weren't told to do it during the course, either.

Ironically, I got >299 M Ohms on my N-E test, but I do know why you're saying you should disconnect.

I can't understand why it didn't show up the fact that they are connected on the test. Any ideas?


It's alright, it's just come to me.

The 2391 board had a seperate 'main isolator' which was probably 4-pole.

When the assessor opened this, it will have disconnected the neutral as well:)
 
Last edited by a moderator:
The 2391 board had a seperate 'main isolator' which was probably 4-pole.

When the assessor opened this, it will have disconnected the neutral as well:)

You beat me to it. I suspect that is what has happened. When I did it we certainly had to break the link.
 
im doing am2 on tncs do i have to remove the main neutral out of bar or take each one out and on my lighting circuit do i only flick the switches on whichever phase its on thanks
 
im doing am2 on tncs do i have to remove the main neutral out of bar or take each one out and on my lighting circuit do i only flick the switches on whichever phase its on thanks
On single phase installations, the main switch will be double pole.
As such there is no requirement to disconnect the N-E link.
 

Reply to insulation resistance of a 3ph circuit in 2391 in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
810
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
857

Similar threads

Thanks, I was hoping someone could confirm whether it was odd or not. I've done a fair bit of insulation testing but only on a small number of...
Replies
4
Views
283
Continuity of the suspect cable appears fine all cores, from this I could work out the length of it and it really doesn’t appear looking at the...
Replies
2
Views
332

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top