Discuss insulation resistance of a 3ph circuit in 2391 in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Good answer, but what is the FCU?
The 2391 board will be TN-S, if you had a TN-C-S supply you woulld have to remove the neutral test link otherwise you would get continuity between neutral and earth.
You need to break the neutral link on any TN system - TN-S included - for the purposes of an insulation resistance test.
The 2391 board had a seperate 'main isolator' which was probably 4-pole.
When the assessor opened this, it will have disconnected the neutral as well
On single phase installations, the main switch will be double pole.im doing am2 on tncs do i have to remove the main neutral out of bar or take each one out and on my lighting circuit do i only flick the switches on whichever phase its on thanks