insulation resistance of a 3ph circuit in 2391 | Page 2 | on ElectriciansForums
Discuss insulation resistance of a 3ph circuit in 2391 in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
The neutral on that circuit or like the main neutral to the bar?
It depends on how you are testing.
If you are disconnecting the conductors at the CU to test an individual circuit, then it would not matter.
However if you were to conduct a global IR test, you would have to verify that the neutral is disconnected, or you would be testing the IR of the network supply neutral.
Reply to insulation resistance of a 3ph circuit in 2391 in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Thanks, I was hoping someone could confirm whether it was odd or not. I've done a fair bit of insulation testing but only on a small number of...
Continuity of the suspect cable appears fine all cores, from this I could work out the length of it and it really doesn’t appear looking at the...