how would you calculate the insulation resistance on domestic ring circuit when measuring with both live and neutral conductors connected together to the circuit protective conductor, is there any way of calculating the approximate value before using a insulation resistance instrument. cheers
 
I'm not sure I understand the question!

my question was that instead of testing live to earth and neutral to earth separately, connect both conductors to one lead of the tester and other lead to earth, the reason I am asking this question is because recently I was carrying out a test on a ring circuit run in twin and earth, when testing live to earth and neutral to earth separately I obtained values of resistance greater than >9000 when both live and neutral are connected together on one lead of the instrument and the second lead to earth my insulation resistance was less than half on a short test and would increase on a 30 second test, is this just due to the increase in parallel paths.
 
I think what our man means here, is that L & N are in parallel, so you could expect half the single L/N-E test results.
Also, twice the cable length under test, so it'd take longer to charge up.


Disclaimer, it's late and I've had loadsa beer! :)
 
You can as a minimum IR between live conductors to CPC. Preferable to do all three though. Zap L - N at 250V to see if anything may still be connected. But, No, you can't calculate IR test results, have to measure them..

Are you getting mixed up with r1r2/4 continuity tests etc perhaps?!

Just read your second post, if you are getting >9000 meg ohms for L-CPC and N-CPC then measure L-N and be happy! Don't worry yourself measuring LN-CPC. What tester you using?
Remember in T&E the CPC isn't insulated, which would have a bearing possibly.
 
I am quite certain that there must be calculations that are employed by the cable manufactures to determine the effects of parallel paths and insulation resistance over a given length.
cheers
 
I am quite certain that there must be calculations that are employed by the cable manufactures to determine the effects of parallel paths and insulation resistance over a given length.
cheers

There is a calculation for 'parallel paths' as you call them. We all learned it at school, and then went over it again when training to be electricians. Does 1/R = 1/R1 + 1/R2 + 1/R3 ....... + 1/Rn ring any bells with you?
 
my question was that instead of testing live to earth and neutral to earth separately, connect both conductors to one lead of the tester and other lead to earth, the reason I am asking this question is because recently I was carrying out a test on a ring circuit run in twin and earth, when testing live to earth and neutral to earth separately I obtained values of resistance greater than >9000 when both live and neutral are connected together on one lead of the instrument and the second lead to earth my insulation resistance was less than half on a short test and would increase on a 30 second test, is this just due to the increase in parallel paths.
Just out of interest,when you say "half",do you mean half of >9000 or half a M Ohm? Also,there is a difference between parallel paths and resistances in parallel. The difference between your two IR readings,if known for sure,would help explaining what may be occurring.Thanks
 
Why not just measure IR like normal?

Trev is right why complicate things...... lifes hard enough!!!! :banghead:

Quite simple, the IET’s one size fits all doesn’t fit in the real world.

When you’re faced with 500yards of 0.3²” 3c PILC SWA that’s over 50 years old, are you going to replace it? 0.3 is about 240mm.
A large motor (100’s of HP not some piddling little thing) are you going to replace it?

You work out the minimum acceptable resistance and then use your experience to say if it’s a goer or not.
Before I condemned anything I made damned sure I was right.

Regarding the 50 year old cables, they were that old before I diverted them for reuse 25 years ago. 75 years old and still in service to this day.

Believe it or not dazza, we had electric long before the 17[SUP]th[/SUP] edition.
 

Reply to insulation resistance on a domestic ring circuit in the Domestic Electrician Forum area at ElectriciansForums.net

Similar Threads

I was at the other end of the results spectrum today. As I was driving home I had a call from my "Mrs Richards from Fawlty Towers" lady, very deaf...
Replies
20
Views
1K
  • Question
I may have been mistaken regarding TT I will look into that, thank you for the valued reply, but in general I stick to my post, a good topic for...
Replies
24
Views
3K
  • Question
There can be a few reasons for low L+N -> E readings: Connected equipment is leaking. By design, or just old/damp SPD are connected (but there...
Replies
9
Views
1K
  • Question
He is after the four options for 1 and 2 of the multiple choice exam, probably optimistic someone will know this. Your question 3 in incomplete to...
Replies
2
Views
1K
  • Question
My tester goes up to 2000M ohms and even on brand new wiring it rarely hits that target, sometimes it will show something random like 1746 or...
Replies
7
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks