On initial verification of new installations I have been having a hard time with insulation resistance.

With RCBOs, fixed LED luminaires, intelligent dimmer controls and other sensitive equipment now the norm on almost all installations how do we overcome this and still carry out effective and compliant testing?

I have found it hard to test in the correct sequence. As to verify cpc via R1+R2 everything must be connected, and the removed again before testing IR. In my mind this seems to defeat the point. This is especially true on lighting circuits with intelligent dimmers and fixed LEDs.

I’m not sure of others workarounds/tips, but on these circuits I have taken to not connecting the LEDs/dimmers and wagoing all the connections at the switches and not cutting the bights of cable for downlights, then doing an R2 test at available points to prove cpc(which I don’t record later on paperwork). Then carrying out L-N L-E N-E IR testing. This in my mind then follows the sequence laid out in BS7671

I then install all the sensitive equipment and do my R1-R2 tests as normal (record these values) and then in place of full IR testing just a L+N-E to prove nothing I have just installed has caused any issues. Any one see any problems with this?

Aside from this, on full RCBO boards, I have been testing each circuit individually and calculating the whole board value. On small 6 way boards it works fine, however my tester only reads up to 2000Mohm, so on larger boards the value calculated is below 20Mohm, although in reality much higher. I note this on the paperwork. Anyone do anything different or have any other ideas?
 
TL;DR
How to get round IR testing on modern circuits
The best option would be a globe testing
Line to line and earth on its own at 230v
With out damaging sensitive equipment.
Has for megg reading then the onside guide will give you the values.
 
I use click connectors for all spots so can just unplug them. Then for all light fittings, mount the bases, strip back and Wago. IR it all then connect it all and R1+R2. Testing I think takes twice as long on initial verification now.
 

Reply to Insulation resistance on modern installations in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hope everyone has had a great Christmas and here’s hoping we all have a better new year coming our way ! Remember our riches aren’t measured by...
    • Friendly
    • Like
Replies
11
Views
511
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
754
  • Sticky
  • Article
Thanks so much for sharing this with us! I’ll definitely take a look, it seems like there are a lot of useful and interesting products. The idea...
    • Like
Replies
5
Views
2K

Similar threads

Continuity of the suspect cable appears fine all cores, from this I could work out the length of it and it really doesn’t appear looking at the...
Replies
2
Views
391
If the main switch is on when testing global IR then the neutral and earth will likely give a very low reading. Not that anyone would...
Replies
10
Views
655
loz2754
L

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top