When doing domestic testing, I spend quite a bit of time removing loads & vulnerable equipment prior to carrying out IR tests- allowing me to test between L - N without risk to vulnerable equipment or getting inaccurate readings. I’ve spoken to a number of sparks who go straight to testing L&N together to Earth.

I’m interested to know how far you would go to remove vulnerable equipment before opting for the easier test??
 
Given most domestic stuff is wired in T&E with the E between L&N you are likely to see most potential problems with the safe L+N to E testing.

You would still need to deal with any SPD as they are often connected to E but if you see a big difference going 250V to 500V you can be fairly sure they are the reason so look for power blocks with surge protection built in, etc.
 
As @bill01803 says, doing a global L+N -> E test is a good starting point for any checks or before work, as it can be down without disconnecting anything by switching off the main isolator, and if low it warns you that a can of worms is about to be opened.
 
On existing circuits, particularly lighting with downlights, outside lights etc it is simply not practical to test L-N, and I am of the opinion that those who claim to always test L-N are simply lying. I would love to see them go round and disconnect 30 integrated downlights and half a dozen outside lights prior to their 2 minute test. Half a day to disconnect everything, 2 minutes to test and another half a day to reinstate.....Yeah right.
However where new circuits are being tested for initial verification, in most cases it will be practical and correct to test L-N as the layout of the circuit will be known and testing can take place before any loads are connected.
And as has already been stated, with T/E wiring with a bare copper conductor between live conductors it is highly unlikely that a L-N fault would happen without tracking to the bare conductor as well.
 

Reply to Insulation Resistance query in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
380
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
956
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Thanks, I was hoping someone could confirm whether it was odd or not. I've done a fair bit of insulation testing but only on a small number of...
Replies
4
Views
286
Continuity of the suspect cable appears fine all cores, from this I could work out the length of it and it really doesn’t appear looking at the...
Replies
2
Views
349

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top