Just at a job this morning where customer has an RCD that trips whenever it likes with no pattern in when it trips.

Testing lives to CPC found that RFC was showing 10.5 Meg ohms which as opposed to >299 for all other circuits. The only item of equipment that wasn't unplugged due to location of the socket was the Sky box in the bedroom.

I then managed to get the drawer unit pulled forward to unplug the said Sky box then re tested and got >299Meg Ohms. What puzzled me was how can an item of equipment which is double insulated affect Ins Res readings between Live conductors and CPC?
 
Faulty plug/lead?
Have you IR tested the plug/lead?



+tion:

I was thinking if its got a 2 core power lead.
 
Last edited by a moderator:
Is the SKY box still working after you put 500vdc across it ? if then you were lucky also you say the RCD trips anytime I had a job like this and I mentioned to the customer I cannot find the problem so you need to take note of what you were doing when it tripped and a week later I was told it was the dishwasher.
 
Course its still working, why wouldn't it be.

Told them the same, that all fixed wiring was ok so will have to keep an eye on what is being used etc.
 
The aerial coax lead is likely to be grounded to provide a screen for the signal line. A signal ground rather than an electrical ground. This maybe where you are getting lower than expected readings.
 
must be the leakage fairies. don't forget that the neutral is connected to E at source ( TNC-S ) so that could affect your reading .
 
so, it's back to the fairies then. unless it's the coax, as said previously.
 

Reply to Insulation Resistance query in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
311
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
834
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
936

Similar threads

Thanks, I was hoping someone could confirm whether it was odd or not. I've done a fair bit of insulation testing but only on a small number of...
Replies
4
Views
284
Continuity of the suspect cable appears fine all cores, from this I could work out the length of it and it really doesn’t appear looking at the...
Replies
2
Views
333

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top