Insulation resistance results weird on actuator circuits | on ElectriciansForums

Discuss Insulation resistance results weird on actuator circuits in the UK Electrical Forum area at ElectriciansForums.net

Joined
Sep 19, 2023
Messages
26
Reaction score
6
Location
Stoke-on-Trent
Interested in people's thoughts/experience here. I've just been testing out the insulation resistance on a 20 year old surface water pollution control facility. It has a large number of penstocks with Auma actuators.

Here's the puzzle: on a few of them, the resistance - although passable - is conspicuously low at 3-4MR in one case, between phases, but absolutely fine phase to earth. The cables are SWA four core, with CPC and the armour connected to CPC both ends.

I don't see how the insulation resistance can measure 3-15 MR between phases, but several hundred MR or even GR phase-earth in the same cable? Any thoughts? The only thing I can think is if an overcurrent occurred at some point and heated up the phase conductors and left the CPC insulation relatively unscathed? All the actuators are healthy.

The actuators were complete disconnected during the test, of course, so this is purely cable insulation, although there is a plug-type connector on one end that would be onerous to remove.

Interested if people with more experience than me see this all the time or is it odd?
 
It is a bit odd. It's not an essential service that's got a high impedance IT earthing arrangement for first fault tolerance is it? I'd suggest just accurately record all the IR test results and monitor their trends over time.
 
My guess would be moisture at the plug end. Not necessarily wet, but vapour inside the plug. Or if it's a really old cable, could be starting to weather and crack?
On this particular site, when insulation resistance has tested a bit lower that expected - say 50MR - it's always turned out to be due to a rotary isolator in the field, enclosed in a cheap plastic box. As you say, suspect moisture ingress. These are decent quality metal plugs though and everything appears to be watertight. I'm going to have to dismantle a couple of the suspect ones and test literally cable only with nothing whatsoever attached to it except fresh air!
 
It is a bit odd. It's not an essential service that's got a high impedance IT earthing arrangement for first fault tolerance is it? I'd suggest just accurately record all the IR test results and monitor their trends over time.
Thanks, I was hoping someone could confirm whether it was odd or not. I've done a fair bit of insulation testing but only on a small number of sites of similar vintage. No nothing weird and wonderful about the earthing, just a few with weird readings. Unfortunately this is (as far as I know) their first IR test in 20 years so no historical data. I presume they were tested at commissioning but I haven't seen the records.
 

Reply to Insulation resistance results weird on actuator circuits in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
953
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top