Readings that climb as the button is held on are generally down to damp.
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Insulation resistance - strange readings in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Well spotted. The 17th Edition prohibited insulation resistance being tested this way.Mhmm that video has his earth out of the earth bus bar on IR test.
Well spotted. The 17th Edition prohibited insulation resistance being tested this way.Mhmm that video has his earth out of the earth bus bar on IR test.
Think you’ll have to back that statement up with a Reg. No.Well spotted. The 17th Edition prohibited insulation resistance being tested this way.
Because there could be a fault to Earth that isn't to the cpc.Aside from regs you want the earth connected for the "biggest bang" scenario.
P.S. check Regulation 612.3.1 It used to be done with the earth disconnected but there was a change and now it is required to have the earth connected to the bus bar. Can't remember the exact reasoning behind it.
I never suggested that. I voted disagree because the information in the video is incorrect.you swear that I made that video of I/r testing ,risteard .
Don't have Regs book on me until Monday. If you read the section about insulation resistance testing needless to say that's where the regulation is.Think you’ll have to back that statement up with a Reg. No.
It’s as Vortigern says, 612.3.1.Don't have Regs book on me until Monday. If you read the section about insulation resistance testing needless to say that's where the regulation is.
Any damp present?
Did you null the the leads before retesting?
Are there any poor connections, croc clips not making contact properly?