Back in 2013 I had a Domestic Electrical Installation Condition Report done on my rented property - nothing horribly major but one thing I didn't understand...

I had a C3 code for "0 ohms readings for I.R test for sockets & lighting (unable to remove all loads sockets, lighting had electronic dimmers)"

I didn't do anything about this at the time, but 5 years on I'm thinking that cables don't improve with age so perhaps I should get the insulation testing done this time.

So...
1) Yes I have some electronic dimmers, so how do I overcome this? Do they need to be taken off to do the IR testing? And do I need to put ordinary switches back on temporarily, or can I just unscrew the live cable, do the test and put the switches back?
2) I don't understand how sockets would have been a problem, surely it's easy enough to just unplug everything. Was the tester just being lazy, or is there another problem that isn't really being explained?

Thanks
Phil
 
Im not after the limitations or i woukd be asking for page 1. Im after the deviations that he has found on his EICR.
Ok but a deviation is a design decision made that doesn't comply with the regs but provides an equivalent level of safety to that which would comply.
If they were listed on the eicr, it would only be a comment referencing the eic. If a non compliance was found it would be given a classification code depending on what kind of danger it posed.
 
I think this time round I'll be there when it's done. Sounds like I need to be!

S'funny, 20-30 years ago when you hired an expert you just left them to get on with it, nowadays you need to have a much higher degree of understanding to even define the job that needs to be done. But that's getting a bit philosophical...

This is for my house in UK, but where I (mainly) live in Azerbaijan all tradesmen are called "meister" - but most of the time I know more about how to do the job than they do.
 
Maybe they have TNC installations in Azerbaijan?
This is my house in Reading!

In Azerbaijan many, even most, houses are wired without earth cables at all. I have a 3 phase supply with 4x16mm aluminium cores. I put two large earth rods in the garden. The house is wired with T&E and CU imported from the UK, apart from first fix I did most of it myself, including learning to strip 4x35mm SWA.

But over in the thread where you post photos of bad installations I added some pics of the usual standards here.
 
and then test L to N at 250V
I don't ever test between live conductors during a periodic inspection. It's not remotely feasible. It is always an agreed limitation of mine. (If they declined the agreed limitation then it would have a very large upward effect on the quoted price.)
 
The IR columns are headed MΩ, so a reading of '0' strictly means 'less than 500kΩ to one significant figure' but I don't think whoever wrote that thing understood such subtleties. Since an L-N reading of '0MΩ' could range from 500kΩ (non compliant but might be relatively safe) to 100Ω (probably on fire) to 1Ω (can't close the MCB) it's obviously not a helpful result to give and a bit more work is required during testing to find out what the actual resistance is.

And then there's the likely numpty-factor behind the N-E readings. I bet there's one N-E fault, the tests were done with all the N's still connected, and the circuits reading '0MΩ' for L-E still had load on so the line could see through to the neutral fault.
 

Reply to Insulation resistance test issue in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
438
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
There can be a few reasons for low L+N -> E readings: Connected equipment is leaking. By design, or just old/damp SPD are connected (but there...
Replies
9
Views
2K
  • Question
I may have been mistaken regarding TT I will look into that, thank you for the valued reply, but in general I stick to my post, a good topic for...
2
Replies
24
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top