Can any one explain to me the correct method to test insulation resistance on a 3 phase consumer unit all at once as apposed to testing each final circuit individually?

Especialy circuits vulnerable to test voltage. GN3 states that you connect line and neutral together and test to eath is that all three line conductors an neutral at once or individually?
 
With the DB main switch off and all mcb's on...
test from L1 to E
L2 to E
L3 to E
N to E
test from the output side of the main switch terminals and record the lowest reading
Use 250v test voltage first if equipment may still be connected , then 500v if all clear.
 
The OP doesn't state if this is a new install or a PIR type test, test method 1 for new installs, test method 2 is acceptable for existing installs if equipment can not be disconnected, in fact so is a 250 V test acceptable
J
 
The OP doesn't state if this is a new install or a PIR type test, test method 1 for new installs, test method 2 is acceptable for existing installs if equipment can not be disconnected, in fact so is a 250 V test acceptable
J

If connected equiment is mentioned , i'd guess periodic
new install would be tested before equipment is connected.
usually lol.
 
Sorry should have stated, its for the insulation resistance testing part of the 2391 practical test ,our tutor mentioned this is somtimes the method you are asked to use. Not sure on the scenireo i.e initial/periodic? of install?
 
If connected equiment is mentioned , i'd guess periodic
new install would be tested before equipment is connected.
usually lol.

Well yes you would hope so ! but how many peeps test through the tails on a new install and push 500V through the rcbo's or RCD's ? not something I would want to do ! LMAO
J
 
I think its a myth worrying about 500v tbh - when I did my 2391 (passed) we were told not to p**s about worrying about that.


EDIT; i meant specifically through RCDs.
 
I think its a myth worrying about 500v tbh - when I did my 2391 (passed) we were told not to p**s about worrying about that.


EDIT; i meant specifically through RCDs.

I still wouldnt risk 500v between L-N though if i thought electronics were connected somewhere.
 
If I'm testing on the unknown, I always do the first buzz at 250v, that way you can see from a very low reading if you need to look harder. Likewise, when doing a new install I put a little flag marker on the cable of any circuits where care is needed.
 
jimmy would you ir circuts individually ive ir through rcbos and rcds before and had no problems what problems are you thinking you could have

Sorry for the late reply, I have had a long chat with MK technical today, and they assure me that for the purposes of the regs and the application of the regs, RCD's and RCBO's are classed as containing electronic components and should not be subjected to a 500V test, and of course any impedance in the components might skew your readings,think about the description of the test, 'Insulation resistance test' we are testing the integrity of the insulation between live conductors and Earth, we are not testing the integrity of component parts of the installation, ( although I except defects in accessories may well show as a fault) so I will continue to test them from the load side not the supply side.
J
 
10 point test same as 'Safe Isolation'.

L's - L's
L's - Ns
L's - E's
N - E

Probably a vulnerable 3 phase motor circuit.
Tails are not to be tested as it's EICR not new install.

Plus they'll be connected to incoming supply for live tests later on.

I tested from busbar terminals of main switch, all MCB's on.
Secondary CSU main switch off.

Didn't test through RCD's or RCBO's.

Rememeber CRIPPLER and it's easy.
 
Last edited by a moderator:
Oh yeah, forgot.

There is a small IR test rig where you have to find what sort of fail it is, dead short etc.. and on which circuit.

This is only single phase tho and the rigs are the same across all centres I think.

Never heard of cross connecting 3 phase on 2391.

But I may be wrong...
 
Word of advice, in your testing exams do not use the term "dead short" C&G are very particular about terminology. It's a short cicuit, nothing more nothing less.
 

Reply to Insulation resistance test on a whole consumer unit?HELP in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
317
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
842
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
965

Similar threads

Thanks, I was hoping someone could confirm whether it was odd or not. I've done a fair bit of insulation testing but only on a small number of...
Replies
4
Views
284
Continuity of the suspect cable appears fine all cores, from this I could work out the length of it and it really doesn’t appear looking at the...
Replies
2
Views
333

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top