L
Lilyrose08
Iam currently on a new build project and I've been carrying out some IR test prior to everything being boarded up. The construction is all timber frames with celotex ply and plaster board, I have connected up the kitchen ring with connector blocks to carry out IR tests and I have been getting low readings for a new install L/E 50Meg N/E 45Meg and L/N about the same the readings do increase when you hold test button down.
Do u think these low readings could be down to damp and moisture in the air as it is a building site and very cold and exposed.
Im a little bit concerned as I normally expect greater than 50Meg
any ideas anyone would help
thanks
Do u think these low readings could be down to damp and moisture in the air as it is a building site and very cold and exposed.
Im a little bit concerned as I normally expect greater than 50Meg
any ideas anyone would help
thanks