Insulation resistance test on new circuit | on ElectriciansForums

Discuss Insulation resistance test on new circuit in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

L

Lilyrose08

Iam currently on a new build project and I've been carrying out some IR test prior to everything being boarded up. The construction is all timber frames with celotex ply and plaster board, I have connected up the kitchen ring with connector blocks to carry out IR tests and I have been getting low readings for a new install L/E 50Meg N/E 45Meg and L/N about the same the readings do increase when you hold test button down.
Do u think these low readings could be down to damp and moisture in the air as it is a building site and very cold and exposed.
Im a little bit concerned as I normally expect greater than 50Meg
any ideas anyone would help
thanks
 
If its rising when you hold down the test button, I would suspect damp.
i wouldn't worry about the readings you are getting.
 
If this is testing pre 2nd fix and cables are joined with connector blocks, then how can damp effect things really?

Ok if sockets have been fitted and screwed back and walls are of backing plaster/skim, I can fully understand damp cuasing an issue in the backs of sockets.
 
Lilyrose08

I would be tempted to take the couple of hours on the chin this time & break the ring into two legs, test each, then narrow down which half is providing the low reading & hunt the cause down. When you have found it, and can see it, you will be well chuffed.

Ps lets face it, the damp is a guess!
 
Last edited by a moderator:
If just testing one new circuit I would also expect this to have a reading off the scale, take a bit of time, break the circuit down and find which part is giving the low readings
 

Reply to Insulation resistance test on new circuit in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
330
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
855
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
975

Similar threads

Continuity of the suspect cable appears fine all cores, from this I could work out the length of it and it really doesn’t appear looking at the...
Replies
2
Views
333
If the main switch is on when testing global IR then the neutral and earth will likely give a very low reading. Not that anyone would...
Replies
10
Views
599
loz2754
L

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top