Insulation resistance test on new circuit | Page 2 | on ElectriciansForums
Discuss Insulation resistance test on new circuit in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
YOU CAN NOT BE A SPARK SO WHY ARE YOU TESTING, WHAT A LAUGH, THOSE READINGS TO ME AS A SPARK ARE FINE. NEW BUILD 2 MEG OHMS OLD 1.75 IS LEGAL MEG OHM IS VERY LARGE
MΩ one million ohms
MΩ one million ohms
Cetainly is large.
Not large enough for me though :kiss:
If you were working for me, and presented an EIC with the new circuit readings as 2M Ohms, you'd be going back and finding out why.
But each to their own !
on newly installed wiring 2 meg is certainly not acceptable.
but 50 meg on newly plastered walls is pretty good and will certainly climb after a drying period.
liking the new avatar sparty.
moddeydhoo
as I said, not high enough for me, for a new circuit. Different when reporting on an existing install. It also says just below your quoted reg
"Insulation resistance values are usually much higher than those of Table 61"
Regulations are that, regulations. In effect a guide. The values in Table 61 are the minimum. If they are that low or lower than the infinite reading on your Megger / Fluke / Robin / whatever then ... there is a reason!
the other point I was trying to make to the OP was that it is better to find the fact for the low reading rather than just hoping it will be ok! Facts are good with electrical installations. Guessing is not
I have been testing for years and years, 1 meg ohm, i would take a look for damp or damage on a circuit, simple to brerak down, and test, over 2 would not waste my time, stick it to 10o0v and test 99 times out of 100 the ohms will rise, damp.
I've always worked on the principle that it's better to track down the cause of unexpected readings. Even if the only thing it does is satisfy my curiosity and improve my knowledge.
If it turned out to be a crushed/damaged cable better to deal with it now than later.
Joiners have a terrible habit of trapping cables when putting up plasterboard etc.
On any NEW installation that is having it's first or initial recorded circuit IR tests, then you should always be testing for at least a 1 minute duration. Those lower than expected values will almost certainly be due to the surrounding damp conditions. Another very good reason to take 1 minute IR readings rather than the usual few seconds....
i've come accross this too, and after much consideration I just put it down on the cert. last month i done one and all circuits were around 100M and rising L+N - E but it was just plastered that day so what can you expect.
Reply to Insulation resistance test on new circuit in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
That would depend on the instrument. On my old BM10 when you press & hold the button it just powers up the inverter circuits to generate the...
Continuity of the suspect cable appears fine all cores, from this I could work out the length of it and it really doesn’t appear looking at the...