OP
Graeme Harrold
Was that with line and neutral connected together, and only tested to cpc?
Yes, thats how most machines work, they link L and N internally and buzz between that and earth.
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Insulation Resistance Test One or Two? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Was that with line and neutral connected together, and only tested to cpc?
I was not aware that you need to do a 250 V DC test first if you have removed vulnerable equipment....
I completely disagree, as nothing can flow through the equipment because the voltage cannot see (i.e. no potential difference) the equipment as the line and neutral are connected together. All that will be picked up is any insulation faults between the cpc and either of the live conductors, which is what you want to see.
Sorry folks quoted the BRB of the top of my head correct one is 612.3.3 and I agree with the above no need to use 250v
Chris
That would be because you don't have to!
Have to agree with those who err on the side of caution and use 250v. Big difference in my book between a periodic and a new installation. That's why the limitations gets a regular workout on Pir's.
Most definitely limititations should be used for PIR's, but I have yet to cause any problems using the 500V with line and neutral connected tested to protective earth. 250V doesn't always show up an insulation fault, due to the reason as previously stated with 250VDC not being the same as 250VAC.
But I suppose it's better than doing no test at all, which I often find when I see periodics with >299M across the board, as from experience testing a whole board on a periodic you will not often find such a perfect reading...
Anybody who has ripped apart a 30 year old installation to make sure they do a comprehensive test report may one day bite off more than they can chew, been there and it wasn't pretty!!!
The lowest acceptable limit is as we know is 1MO. Thats a resistance of 1000 O.
No current will be flowing out of the wire , IMO.