K

Kev2632

Hello,

im reading up on the insulation resistance test at the moment, when doing an insulation test on say a ringmain, and there is switched fused switches with neon, and the switch is OFF, can this still affect the reading? also when doing the L to N, why is it sometimes get really low reading of 0.01ohms, when everything is unplugged?. whats the reason for that?

Thanks.
 
The Neon should'nt have any effect as long as the Spur is off, the Neon is fitted across the load side to show when it's turned on.

An 0.01R reading on an Insulation test is a S/C it could be caused by wires not correctly terminated & touching etc.
 
I'm not sure about the switched fused units you have but I've come across those 5 into 1 plug banks where the neons are wired between the live and earth.

The thing with neons in circuit is that if they're between live and earth they'll actually illuminate during the IR test so they're easy to spot.
 
Hi Marvo: A switched fused spur is a Switch with an inbuilt fusehoder, used over here on the supply to such things as Burglar Alarms, Heating systems etc.
 
L-N Reading of 0.01 usually means you have missed an outlet. I find it in kitchens where sockets are in cupboards and often miss the Hob ignition and extract. For this reason I usually test at 230v first so as not to damage any equipment
 
Last edited:
L-N Reading of 0.01 usually means you have missed an outlet. I find it in kitchens where sockets are in cupboards and often miss the Hob ignition and extract.

Thanks mate: I forgot about that, for some reason I thought he was talking about new cct's. Oh well they say old age don't come alone lol.
 
Hi Marvo: A switched fused spur is a Switch with an inbuilt fusehoder, used over here on the supply to such things as Burglar Alarms, Heating systems etc.

sorry to be picky, but alarm systems use an unswitched FCU
 
Do you think that Glenn possibly missed the bit about the RFC ? Have you turned off all sockets / spurs ? & checked for hidden sockets / spurs behind units in the kitchen ? Kitchen fitters have a habit of doing this. Also check in the airing cupboard if there is 1 to make sure the immersion is not tapped off the ring or as 1 i found today the central heating wiring chopped into the ring & taken into a landing cupboard.
 

Reply to Insulation Resistance Test?? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
351
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
898
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Continuity of the suspect cable appears fine all cores, from this I could work out the length of it and it really doesn’t appear looking at the...
Replies
2
Views
339
  • Question
There can be a few reasons for low L+N -> E readings: Connected equipment is leaking. By design, or just old/damp SPD are connected (but there...
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top