Hello,

im reading up on the insulation resistance test at the moment, when doing an insulation test on say a ringmain, and there is switched fused switches with neon, and the switch is OFF, can this still affect the reading? also when doing the L to N, why is it sometimes get really low reading of 0.01ohms, when everything is unplugged?. whats the reason for that?

Thanks.
 
The Neon should'nt have any effect as long as the Spur is off, the Neon is fitted across the load side to show when it's turned on.

An 0.01R reading on an Insulation test is a S/C it could be caused by wires not correctly terminated & touching etc.
 
I'm not sure about the switched fused units you have but I've come across those 5 into 1 plug banks where the neons are wired between the live and earth.

The thing with neons in circuit is that if they're between live and earth they'll actually illuminate during the IR test so they're easy to spot.
 
Hi Marvo: A switched fused spur is a Switch with an inbuilt fusehoder, used over here on the supply to such things as Burglar Alarms, Heating systems etc.
 
L-N Reading of 0.01 usually means you have missed an outlet. I find it in kitchens where sockets are in cupboards and often miss the Hob ignition and extract. For this reason I usually test at 230v first so as not to damage any equipment
 
Last edited:
L-N Reading of 0.01 usually means you have missed an outlet. I find it in kitchens where sockets are in cupboards and often miss the Hob ignition and extract.

Thanks mate: I forgot about that, for some reason I thought he was talking about new cct's. Oh well they say old age don't come alone lol.
 
and the obvious one of course.....connected loads such as showers etc......these will give off fake readings.....
 
yea but why would a shower or that affect the ring main that is being tested at the moment?
 
Hi Marvo: A switched fused spur is a Switch with an inbuilt fusehoder, used over here on the supply to such things as Burglar Alarms, Heating systems etc.

sorry to be picky, but alarm systems use an unswitched FCU
 
could even be a cooker hood with it's plug and socket inside the chimney.
 
Do you think that Glenn possibly missed the bit about the RFC ? Have you turned off all sockets / spurs ? & checked for hidden sockets / spurs behind units in the kitchen ? Kitchen fitters have a habit of doing this. Also check in the airing cupboard if there is 1 to make sure the immersion is not tapped off the ring or as 1 i found today the central heating wiring chopped into the ring & taken into a landing cupboard.
 
sorry to be picky, but alarm systems use an unswitched FCU

That is the normal way.....
One local company around here (actually just stopped trading) I had a big time argument about segregation of safety circuits, as they would not accept it exists, until the BRB came out.
 
Do you think that Glenn possibly missed the bit about the RFC ? Have you turned off all sockets / spurs ? & checked for hidden sockets / spurs behind units in the kitchen ? Kitchen fitters have a habit of doing this. Also check in the airing cupboard if there is 1 to make sure the immersion is not tapped off the ring or as 1 i found today the central heating wiring chopped into the ring & taken into a landing cupboard.
yea checked everywhere!!, there was no other appliances plugged in at all, would other circuits on the rcd affect the ringmain that is being tested?
 
sorry to be picky, but alarm systems use an unswitched FCU

You've obviously led a sheltered life mate, Alarm systems are supposed to use an Unswitched fused spur. Unfortunately a lot of Installers don't know the difference & fit Switched. I used to carry 20 unswitched on the van with me we were changing so many of them after subbies.
 
Last edited by a moderator:
what regs says you need a unswitched fused unit for an alarm ?
 
Last edited by a moderator:
Did you disconnect the RFC conductors at the CU & check ?

nope, dont normal have too, but can anybody answer this one" if you are testing at the Consumer on the 1 side of the RCD, and everything is isolated are you are doing L-N on the ringmain, will other circuits on that RCD affect the result of the circuit being tested????
 
nope, dont normal have too, but can anybody answer this one" if you are testing at the Consumer on the 1 side of the RCD, and everything is isolated are you are doing L-N on the ringmain, will other circuits on that RCD affect the result of the circuit being tested????[/

If you find what you think is a fault on an insulation test of any circuit then the first thing to do is completely isolate it from the board & test again.
 
nope, dont normal have too, but can anybody answer this one" if you are testing at the Consumer on the 1 side of the RCD, and everything is isolated are you are doing L-N on the ringmain, will other circuits on that RCD affect the result of the circuit being tested????[/

If you find what you think is a fault on an insulation test of any circuit then the first thing to do is completely isolate it from the board & test again.


Thanks for that, but if you are testing at the Consumer on the 1 side of the RCD, and everything is isolated are you are doing L-N on the ringmain, will other circuits on that RCD affect the result of the circuit being tested???
 
As posted before, Remove all cables from CU if you are getting these sort of readings and re test. Other circuits may have an effect as the neutral and earth will be linked as you are only isolating the line between circuits.
 
Thanks for that, but if you are testing at the Consumer on the 1 side of the RCD, and everything is isolated are you are doing L-N on the ringmain, will other circuits on that RCD affect the result of the circuit being tested???

I see what you are saying, and as long as all other MCB's, RCD's and the isolator switch are open.

However, is there only the one ring circuit?
I think you have to disconnect and confirm continuity as someone may have done a mix up of cables in the consumer unit.
 
As posted before, Remove all cables from CU if you are getting these sort of readings and re test. Other circuits may have an effect as the neutral and earth will be linked as you are only isolating the line between circuits.

Yea thats very true, doesnt some switches like 13amp switches fused, cooker switches, shower switches always isolate the neutral as well?
 
I see what you are saying, and as long as all other MCB's, RCD's and the isolator switch are open.

However, is there only the one ring circuit?
I think you have to disconnect and confirm continuity as someone may have done a mix up of cables in the consumer unit.

Yea just 1 ringmain doing the whole house, but when you disconnect the circuit and checking for continuity are you meaning just Ring Continuity aye?
 
Yes, to make sure that is the ring and not mixed with another ring or spur by some previous meddler.
 
Yes, to make sure that is the ring and not mixed with another ring or spur by some previous meddler.


Yea thats very true, it just had my head scratching today, because ive never really had such a low reading on L-N before, but it seems common
 
Thanks for that, but if you are testing at the Consumer on the 1 side of the RCD, and everything is isolated are you are doing L-N on the ringmain, will other circuits on that RCD affect the result of the circuit being tested???

If you want to do an Insulation test on a Circuit from the CU: Isolate by opening the Main Switch / RCD, Turn off all MCB's. Test from the Circuit side of the MCB with everything Switched off, if you have a low resistance between any conductors on the circuit you are testing then identify the L/N/E for that circuit & remove from the CU. Now do your Insulation test again to see if the fault still remains, if it does then re-check that everything on the circuit is definately turned off / unplugged. If you prove that everything is disconnected then you can start looking for a fault.
 
what regs says you need a unswitched fused unit for an alarm ?

Pardon ? Take a look back as far as BS4737 or EN50131, basically you don't supply power to an Alarm via a Plug top or a Switched FCU. Should allways be supplied via an Unswitched FCU with a 3 amp fuse fitted.
 
Pardon ? Take a look back as far as BS4737 or EN50131, basically you don't supply power to an Alarm via a Plug top or a Switched FCU. Should allways be supplied via an Unswitched FCU with a 3 amp fuse fitted.

where does it say this please , i would like to know what reg number
 
where does it say this please , i would like to know what reg number

Sorry mate: I have'nt got a copy of the Regs here with me otherwise I would have posted it up in answer to your original question. If you fit Alarms how do you supply power to them ? You may find a Browsable copy of the Regs on the BSIA website.
 
if the alarm was wired through an unswitched fused unit spurred from a rfc then where would be the point of isolation for maintenance? the cb maybe ...it inconvenient though is nt it..
i would prefere a sfu with a label myself
 
there is not a reg for this btw :cool3: not in BS 7671 and BSIA dont have regs as such not ones that would be used in court to confirm compliance with the statutory regs such EAWR etc at least this my understanding
 
if the alarm was wired through an unswitched fused unit spurred from a rfc then where would be the point of isolation for maintenance? the cb maybe ...it inconvenient though is nt it..
i would prefere a sfu with a label myself

But then your Alarm Installation would'nt conform to EN50131 would it ? I've been to many sites where Alarms are fed through an SFCU all nicely labelled & you get a call to say the Alarm is Dead, only to find after getting there that someone turned the Switch off & the Battery has now gone dead as well. What's the point of a security system where you've got a means of turning it off Right by it ? To isolate the panel you don't need to go to the Circuit breaker you just lift the fuse.
 
there is not a reg for this btw :cool3: not in BS 7671 and BSIA dont have regs as such not ones that would be used in court to confirm compliance with the statutory regs such EAWR etc at least this my understanding

Don't know whats on the BSIA site now, not been on there for a long time but you used to be able to pull them up.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Insulation Resistance Test??
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
43

Advert

Thread statistics

Created
Kev2632,
Last reply from
richardg,
Replies
43
Views
16,390

Advert

Back
Top