Do you think that Glenn possibly missed the bit about the RFC ? Have you turned off all sockets / spurs ? & checked for hidden sockets / spurs behind units in the kitchen ? Kitchen fitters have a habit of doing this. Also check in the airing cupboard if there is 1 to make sure the immersion is not tapped off the ring or as 1 i found today the central heating wiring chopped into the ring & taken into a landing cupboard.
yea checked everywhere!!, there was no other appliances plugged in at all, would other circuits on the rcd affect the ringmain that is being tested?
 
sorry to be picky, but alarm systems use an unswitched FCU

You've obviously led a sheltered life mate, Alarm systems are supposed to use an Unswitched fused spur. Unfortunately a lot of Installers don't know the difference & fit Switched. I used to carry 20 unswitched on the van with me we were changing so many of them after subbies.
 
Last edited by a moderator:
Did you disconnect the RFC conductors at the CU & check ?

nope, dont normal have too, but can anybody answer this one" if you are testing at the Consumer on the 1 side of the RCD, and everything is isolated are you are doing L-N on the ringmain, will other circuits on that RCD affect the result of the circuit being tested????
 
nope, dont normal have too, but can anybody answer this one" if you are testing at the Consumer on the 1 side of the RCD, and everything is isolated are you are doing L-N on the ringmain, will other circuits on that RCD affect the result of the circuit being tested????[/

If you find what you think is a fault on an insulation test of any circuit then the first thing to do is completely isolate it from the board & test again.
 
nope, dont normal have too, but can anybody answer this one" if you are testing at the Consumer on the 1 side of the RCD, and everything is isolated are you are doing L-N on the ringmain, will other circuits on that RCD affect the result of the circuit being tested????[/

If you find what you think is a fault on an insulation test of any circuit then the first thing to do is completely isolate it from the board & test again.


Thanks for that, but if you are testing at the Consumer on the 1 side of the RCD, and everything is isolated are you are doing L-N on the ringmain, will other circuits on that RCD affect the result of the circuit being tested???
 
As posted before, Remove all cables from CU if you are getting these sort of readings and re test. Other circuits may have an effect as the neutral and earth will be linked as you are only isolating the line between circuits.
 
Thanks for that, but if you are testing at the Consumer on the 1 side of the RCD, and everything is isolated are you are doing L-N on the ringmain, will other circuits on that RCD affect the result of the circuit being tested???

I see what you are saying, and as long as all other MCB's, RCD's and the isolator switch are open.

However, is there only the one ring circuit?
I think you have to disconnect and confirm continuity as someone may have done a mix up of cables in the consumer unit.
 
As posted before, Remove all cables from CU if you are getting these sort of readings and re test. Other circuits may have an effect as the neutral and earth will be linked as you are only isolating the line between circuits.

Yea thats very true, doesnt some switches like 13amp switches fused, cooker switches, shower switches always isolate the neutral as well?
 
I see what you are saying, and as long as all other MCB's, RCD's and the isolator switch are open.

However, is there only the one ring circuit?
I think you have to disconnect and confirm continuity as someone may have done a mix up of cables in the consumer unit.

Yea just 1 ringmain doing the whole house, but when you disconnect the circuit and checking for continuity are you meaning just Ring Continuity aye?
 

Reply to Insulation Resistance Test?? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
354
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
905
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Continuity of the suspect cable appears fine all cores, from this I could work out the length of it and it really doesn’t appear looking at the...
Replies
2
Views
344
  • Question
There can be a few reasons for low L+N -> E readings: Connected equipment is leaking. By design, or just old/damp SPD are connected (but there...
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top