Do you think that Glenn possibly missed the bit about the RFC ? Have you turned off all sockets / spurs ? & checked for hidden sockets / spurs behind units in the kitchen ? Kitchen fitters have a habit of doing this. Also check in the airing cupboard if there is 1 to make sure the immersion is not tapped off the ring or as 1 i found today the central heating wiring chopped into the ring & taken into a landing cupboard.
yea checked everywhere!!, there was no other appliances plugged in at all, would other circuits on the rcd affect the ringmain that is being tested?
sorry to be picky, but alarm systems use an unswitched FCU
You've obviously led a sheltered life mate, Alarm systems are supposed to use an Unswitched fused spur. Unfortunately a lot of Installers don't know the difference & fit Switched. I used to carry 20 unswitched on the van with me we were changing so many of them after subbies.
Did you disconnect the RFC conductors at the CU & check ?
nope, dont normal have too, but can anybody answer this one" if you are testing at the Consumer on the 1 side of the RCD, and everything is isolated are you are doing L-N on the ringmain, will other circuits on that RCD affect the result of the circuit being tested????
nope, dont normal have too, but can anybody answer this one" if you are testing at the Consumer on the 1 side of the RCD, and everything is isolated are you are doing L-N on the ringmain, will other circuits on that RCD affect the result of the circuit being tested????[/
If you find what you think is a fault on an insulation test of any circuit then the first thing to do is completely isolate it from the board & test again.
Thanks for that, but if you are testing at the Consumer on the 1 side of the RCD, and everything is isolated are you are doing L-N on the ringmain, will other circuits on that RCD affect the result of the circuit being tested???
As posted before, Remove all cables from CU if you are getting these sort of readings and re test. Other circuits may have an effect as the neutral and earth will be linked as you are only isolating the line between circuits.
I see what you are saying, and as long as all other MCB's, RCD's and the isolator switch are open.
However, is there only the one ring circuit?
I think you have to disconnect and confirm continuity as someone may have done a mix up of cables in the consumer unit.
Yea thats very true, doesnt some switches like 13amp switches fused, cooker switches, shower switches always isolate the neutral as well?
Yea just 1 ringmain doing the whole house, but when you disconnect the circuit and checking for continuity are you meaning just Ring Continuity aye?
Reply to Insulation Resistance Test?? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
That would depend on the instrument. On my old BM10 when you press & hold the button it just powers up the inverter circuits to generate the...
what is the piece of equipment and part number?