While we are on the subject of IR test just a question about R1 R2 jump leads. What cable size do you tend to use if you have made your own?
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Insulation Resistance testing - again! in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
All understood now As wasnt seeing all the new replies (refresh button is a great invention) - So obviously taking the line cables out of fCU and switching FCU to on will then keep circuit but bypass the neon indicator light.
Got it.
Thanks everyone.
You won't need to switch the fcu to anything. The cables will be joined outside the fcu.
Yes, if you don't know that you have continuity of conductors how would you know that your IR test is testing all of the circuit?Kind of related to the above thread.
I am doing the 2391 practical tommorow, to speed up my testing on a rig is there a problem with doing the Insulaion testing prior to the continuity for the Periodic?
Don't confuse EIC (Electrical Installation Certificate--on first install) with EICR (Electrical Installation Condition Report--subsequent test).Its still a periodic inspection and test but you use the EICR to make the report.
I know you need to do it in order for new installations but I don't think you need a particular order for the periodic, I was just trying to figure out if I would be penalised for trying to do the IR on the motor circuit first when I connect across the switch.
Generally, the hybrid nature of the 2391 test rig would mean that you do continuity before IR. However, on a real job, where you know everything is working beforehand then you would be interested in the Zs, without disconnecting all the circuits. So its justifiable to IR test and then Zs.
Just because its all working does not mean you have continuity of protective conductor which is what you test for.Generally, the hybrid nature of the 2391 test rig would mean that you do continuity before IR. However, on a real job, where you know everything is working beforehand then you would be interested in the Zs, without disconnecting all the circuits. So its justifiable to IR test and then Zs.
Just because its all working does not mean you have continuity of protective conductor which is what you test for.
As stated earlier, done in logical sequence so we dont have to redo earlier tests if a fault is found