Hello all, I hope you're all keeping well.

I have a question regarding insulation resistance testing.

Whether doing a single circuit IR test or a global IR on an entire installation, I usually try to remove all loads, eg lamps, neons etc, but obviously this isn't always possible. So I generally join both L+N and test to earth. This is to avoid damaging any sensitive equipment by ensuring no potential difference across the load.

But how come I still can get a bad reading on a circuit while testing this way? I don't fully understand. Is it due to certain loads being able to throw up a bad IR reading and others not?

Any help would be greatly appreciated
 
If this is a global reading you need to break it down to individual circuits by disconnecting the neutral conductors and having all protective devices off. What test voltage are you using.
Having something still connected should not matter unless that something itself is faulty.
 
Some older RCD sockets/spurs will give a low IR to E, without apparently being defective. Surge protection (eg extension leads) will give a low IR when tested at 500V (but not at 250), typically about 0.4M ohms. Anything with a functional earth will again give a low IR to E, in my experience this is only likely to be certain RCDs or RCBOs at a downstream CU.
 
There can be a few reasons for low L+N -> E readings:
  • Connected equipment is leaking. By design, or just old/damp
  • SPD are connected (but there you get a big difference between 250V where usually > 10M and 500V where usually < 0.1M)
  • Cable has degraded or is very damp
  • Accessories are damp/dusty
If a global IR is good, as in above a few M, then you know all circuits are similar.

If the global IR gives you cause for concern, say as it is < 1M, then checking individual circuits can at least establish if a low total is due to, say, 10 decent circuits of ~5M leading to ~0.5M, or 9 are > 10M and one is deeply suspect as different at ~0.5M, etc.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Cork
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
Ireland
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
Insulation resistance testing live conductors to earth
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
9
Unsolved
--

Advert

Thread statistics

Created
An Buachaillín Bán,
Last reply from
pc1966,
Replies
9
Views
2,572

Advert

Back
Top