Advice or quicker ways for doing i r tests on an eicr generally what I have been doing over the years is live to earth neutral to earth and joining live and neutral together then testing to earth job done but my pal who has recently had his annual nice i c visit said he's been shown a new method of doing it by his inspector using a low ohm clamp meter and applying ohms law bit confused and looking for advice if true how to do this and is it achievable
 
I presume he is trying to measure the Earth leakage. There is merit in this approach but BS7671 doesn't recognise it as an alternative.

Out of curiosity the OP states that he measures phase to Earth and neutral to Earth, and then live conductors connected together to Earth. Why the first two tests and not just the live/Earth test? There could also be a risk of damage to equipment with a phase/Earth and neutral/Earth test which is mitigated by connecting the live conductors together.
 
If I'm honest dill totally agree but my mate was adamant even though he didn't explain it well hence my confusion stick to my old ways though must admit the ir tests can be difficult when some of the 36 way boards are chocker and access to the neutral bars and earth bars are difficult with out stripping the whole board down
 
I mentioned this to our gaffer ages ago,nothing ever came of it.
I think it’s a good idea,especially in a big complex,when doing EICR testing,where disconnecting becomes a headache.
Obviously on easier projects always the right way,is always the best way.concerninhg IR tests.
 
A IR test needs to be done at the relevant voltage as per BS7671, so trying to apply ohms law wont work. Be intresting to know what else the “assesor” doesnt know.
Yes very well said Dillb
 
Testing Line to Earth then testing Neutral to Earth, is fine if you then test between Line and Neutral.
Doing three tests to Earth is a waste of time, might just as well do a single test with Line and Neutral joined and test to Earth.
If you’re worried about vulnerable equipment, and can’t be asked to identify, disconnect or link out, then you would do better testing between Line and Neutral at 250V.
 
Advice or quicker ways for doing i r tests on an eicr generally what I have been doing over the years is live to earth neutral to earth and joining live and neutral together then testing to earth job done but my pal who has recently had his annual nice i c visit said he's been shown a new method of doing it by his inspector using a low ohm clamp meter and applying ohms law bit confused and looking for advice if true how to do this and is it achievable
Suggest that your Mate gets a detailed method statement from this NICEIC Bloke
 
IR testing L-N with any loads connected is just pointless. Otherwise they wouldn't be loads ... or have I missed something?
 
Forum got the shakes :)
Yes, I agree the (L+N) to E once there are connected loads. Commenting on post #9 really.
 

Reply to Insulation resistance testing on eicrs in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
380
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
956
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
I may have been mistaken regarding TT I will look into that, thank you for the valued reply, but in general I stick to my post, a good topic for...
2
Replies
24
Views
3K
  • Question
There can be a few reasons for low L+N -> E readings: Connected equipment is leaking. By design, or just old/damp SPD are connected (but there...
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top