When doing a CU change and lights have no cpc. Every room has class 2 dimmers and lights. ceilings are like 20 foot tall. How would you guys go about Insulation testing? L&n to cpc ain't an option and removing all lights and bypassing dimmers is consequently going to take some time... What would you do? Alternitavly ill quote for the time it will take to to do it properly! Basic n-cpc for initial test came back at 67.9m oam


"Apparently they are awaiting on inheritance and will have lights rewired when it comes through"
 
obviously with a note on the cert. and a sticker on the CU. i meant the N/A would be entered on the sotr.
 
you can still do ins. res. tests between L & N upto the switches with the switches in the off position.
i would at least do that than no tests at all.
 
Do the IR test on 250v DC with the dimmer still in the on position. You just need to make a note that you did this because of that reason.

However, that's lazy so just disconnect the dimmers..
 
The fact that there is no CPC is not really a good enough excuse for not conducting an IR test.
Yes where there is sensitive equipment which could be liable to damage, testing between the live conductors and the CPC is acceptable.
However in this instance, there is no CPC available.
As such you sould just bite the bullet and disconnect or link out the sensitive equipment.
As for the lamps creating a short.
They don't create a short if they are removed.
 
The fact that there is no CPC is not really a good enough excuse for not conducting an IR test.
Yes where there is sensitive equipment which could be liable to damage, testing between the live conductors and the CPC is acceptable.
However in this instance, there is no CPC available.
As such you sould just bite the bullet and disconnect or link out the sensitive equipment.
As for the lamps creating a short.
They don't create a short if they are removed.

no but they create a bit of a bang when you drop them off the top of your stepladder.
 
At the very least, take out the bulbs and link out any dimmers. If there's no CPC the IR could be terrible and you need to know this.
 
why do say that lives joined together and test to cpc is not an option, the cpc if it was present would be connected to the MET to include any parallel earths, the joining together of the line and neutral affords the protection for vulnerable equipment, if the I/R test is ok to the MET then no problem, it would then just be a case of checking that all fittings etc are Class 2 at present and advising on a lighting rewire in the future which you have already done



When doing a CU change and lights have no cpc. Every room has class 2 dimmers and lights. ceilings are like 20 foot tall. How would you guys go about Insulation testing? L&n to cpc ain't an option and removing all lights and bypassing dimmers is consequently going to take some time... What would you do? Alternitavly ill quote for the time it will take to to do it properly! Basic n-cpc for initial test came back at 67.9m oam


"Apparently they are awaiting on inheritance and will have lights rewired when it comes through"
 

Reply to Insulation resistance testing with no cpc in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
274
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
269
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
350

Similar threads

Continuity of the suspect cable appears fine all cores, from this I could work out the length of it and it really doesn’t appear looking at the...
Replies
2
Views
298
  • Question
There can be a few reasons for low L+N -> E readings: Connected equipment is leaking. By design, or just old/damp SPD are connected (but there...
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top