That is the required standard when working in Schools and Colleges, particularly in large sports halls and assembly rooms.
 
If you are doing a ccu change you have to issue an electrical installation certificate. This means that the installation must comply with current requirements,meaning, apart from anything else, you lighting ccts must have a cpc. Rather wait until the inheritance comes through and do a proper rewire
 
Even with the lack of a CPC on any particular circuit I would still be testing between L-E and N-E. When conducting IR tests it's called earth for a reason, we're not meggering the CPC, we're meggering the earth, ie. from the line conductor to the earth bar or MET and the same for the neutral conductor. What if somewhere on a circuit with no CPC the cable has been damaged enough through whatever means so that one or other of the conductors are in connection with an exposed or extraneous conductive part? Or what if there's a nice fat screw through the cable linking it to another circuit? In my humble opinion, there's a multitude of reasons why we should still be conducting the IR tests as required.
 
Last edited:
If you are doing a ccu change you have to issue an electrical installation certificate. This means that the installation must comply with current requirements,meaning, apart from anything else, you lighting ccts must have a cpc. Rather wait until the inheritance comes through and do a proper rewire

Not true, The work you do must comply.. You can advice that a cpc / partial rewire is necessary but if thats declined then providing class 2 fittings are used then id be happy to sign it off. Providing of course no further faults were found

This would mean every job that a cert was issued for would be a pricey job wouldnt it.. Carnt insist every install is brought up to current regulations
 
Even with the lack of a CPC on any particular circuit I would still be testing between L-E and N-E. When conducting IR tests it's called earth for a reason, we're not meggering the CPC, we're meggering the earth, ie. from the line conductor to the earth bar or MET and the same for the neutral conductor. What if somewhere on a circuit with no CPC the cable has been damaged enough through whatever means so that one or other of the conductors are in connection with an exposed or extraneous conductive part? Or what if there's a nice fat screw through the cable linking it to another circuit? In my humble opinion, there's a multitude of reasons why we should still be conducting the IR tests as required.

I totally agree. However testing L-Cpc and N-CPC doesnt test the lighting circuits does it if there is no cpc. L-N is the only test which can prove the condition of the cable in this case..
 
I totally agree. However testing L-Cpc and N-CPC doesnt test the lighting circuits does it if there is no cpc. L-N is the only test which can prove the condition of the cable in this case..

If you read my post again you will see that I made a clear distinction between a cable's CPC and Earth in general. When IR testing a cable with no CPC, as well as the obvious L-N test you would carry out on the cable, you should also be carrying out L-E and N-E. Imagine one scenario; the cable has been damaged and the line conductor is exposed and resting neatly on a hot water pipe. How will just a L-N IR test pick this up?
 
If you read my post again you will see that I made a clear distinction between a cable's CPC and Earth in general. When IR testing a cable with no CPC, as well as the obvious L-N test you would carry out on the cable, you should also be carrying out L-E and N-E. Imagine one scenario; the cable has been damaged and the line conductor is exposed and resting neatly on a hot water pipe. How will just a L-N IR test pick this up?

Ah me sees, It wont. Sorry I assumed that you meant this was replacing the L-N test.. N- earth is allways done globally (for me) as it takes less time than doing individually. Only if the reading was less than 2 meg then id be testing individually..

Normally for CCU change and a load of lamps then L/N - Cpc is done globally a) When pricing up and b) When its finished..
 

Reply to Insulation resistance testing with no cpc in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
277
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
269
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
350

Similar threads

Continuity of the suspect cable appears fine all cores, from this I could work out the length of it and it really doesn’t appear looking at the...
Replies
2
Views
298
  • Question
There can be a few reasons for low L+N -> E readings: Connected equipment is leaking. By design, or just old/damp SPD are connected (but there...
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top