stevo09

Can you guys tell me. Would you normaly removed light bulbs whilst do a insulation resistance test. Also what about fittings that use transformers??

Thanks.
 
You can test the board as a whole and cross out the bit on cert that has P-N P-E N-E and write under it P-N + E then on CU link P-N with link wire that way all bulbs trannys etc can be left in ! Sorted !
Also it is exeptable to drop test voltage to 250v for pelv/selv
Or you can remove all bulbs, plugged in equipment, fuses in fused spurs etc and do a 500v test as norm between P-N P-E N-E if no selv/pelv etc but its always good practice to do a 250v test first just in case youve left a bulb in, item plugged in, fuse left in fused spur etc.
 
Last edited by a moderator:
depending on the size of the insallation and number of transformers you could test l-n with the switches open and record a limitation on the cirt
as kung said try 250v first before you damage anything
 
As was mentioned somewhere else here before just remember that the 250V on your meter is probably 250V DC so some electronic equipment will not like it anyway so be careful.
 
just to add, ins res teting is probally the most awkward test to perform in my opinion always get poor readings because there is something you missed still in circuit...
 

Reply to insulation resistance testing in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
810
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
857

Similar threads

Thanks, I was hoping someone could confirm whether it was odd or not. I've done a fair bit of insulation testing but only on a small number of...
Replies
4
Views
283
  • Question
There can be a few reasons for low L+N -> E readings: Connected equipment is leaking. By design, or just old/damp SPD are connected (but there...
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top