Hi all. Changing a CU in an ex-council flat, pme system, no RCD's, and initially tried to IR test whole board L/N joined to earth, got a reading of 0.28 Ohms.

Then did each circuit individually (2 X RFC, 2 X lights, 1 X cooker), L/N joined to the circuit's CPC, and got between 0.25 and 0.30 Ohms on each one.

Any ideas what could be causing the low readings?

Thanks.
 
With the main switch OFF? When you tested the circuits individually, did you remove the N's from the bar? If not, each test was still a global test, and an N-E fault on one circuit will show up on all.
 
Then did each circuit individually (2 X RFC, 2 X lights, 1 X cooker), L/N joined to the circuit's CPC, and got between 0.25 and 0.30 Ohms on each one.
Assuming the individual N was out during each test that is odd. Having a N-E fault on every circuit is a bit more than coincidence and more like an installation with some serious flaws!
 
if the 0.3 ohms reading per circuit is correct a global 0.06 ohms would be a global reading drawing 3.833 KW .either measurement errors , SPDs or item still in circuit (possibly wired incorrectly ) is there an RCD present?
 
Sorry, my mistake - I meant MegaOhms, not Ohms.

No RCDs, no SPDs and an empty property so I couldn't even find anything plugged in. I did the individual tests removing L, N and CPC from the board, so that's why I can't understand why they all had pretty much the same low reading. Wiring is singles in conduit, but can't see how that can make a difference.

It seems there is a problem but I can't even think what that problem might be!
 

Reply to Insulation resistance whole board. in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
748
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
975

Similar threads

Continuity of the suspect cable appears fine all cores, from this I could work out the length of it and it really doesn’t appear looking at the...
Replies
2
Views
424
  • Question
That would depend on the instrument. On my old BM10 when you press & hold the button it just powers up the inverter circuits to generate the...
Replies
5
Views
405

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top