Just wanted to check what min acceptable reading would be when testing a 230v circuit at 250V as opposed to 500V

>0.5 or 1.0> ???

Many Thanks,

Sy
 
Last edited:
this is not for SELV / PELV.... for when you can't do a 500V test on a 230v circuit and use 250V instead ?

Is it the same acceptable reding as selv and pelv then ?

cheers Sy
 
Dont think so, I think you would still need to have at least 1Mohm, maybe one of the other lads can confirm this.

Cheers

Matt
 
SELV & PELV circuits must have a minimum insulation resistance of 0.5 Meg ohms when tested at 250V dc. with all current using equipment disconnected. 612.3.2

Circuits up to 500V must have a minimum insulation resistance of 1.0 Meg ohms when tested at 500V dc with all current using equipment disconnected. 612.3.2

Why are you testing a 230V circuit at 250V?
 
Last edited:
If the circuit contains devices that may be damaged by the test, only a test between the live conductors connected together and the cpc connected to earth is necessary. 612.3.3
 
So why would you test at 250v I remember it coming up at college a few months ago but cannot remember the reason why you would test at 250v.
 
If the circuit contains devices that may be damaged by the test, only a test between the live conductors connected together and the cpc connected to earth is necessary. 612.3.3
So with vulerable equipment it's ok to test at 500v live condutors together and cpc... for some reason I always thought it was a 250v test when there was vulerable equipment..?

Learn something every day
 
if line and neutrtal are connected together, there is no potential difference between the two and currnt cannot flow therfore, so no damage can be caused to connected units.it is a limited test so this has to be recorded on the certificate as a limited test. if the limited test also provides a poor result, then further invstigtion is necessary.
 

Reply to Insulation Resistance.... in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
570
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
999
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
938

Similar threads

  • Question
That would depend on the instrument. On my old BM10 when you press & hold the button it just powers up the inverter circuits to generate the...
Replies
5
Views
381
Thanks, I was hoping someone could confirm whether it was odd or not. I've done a fair bit of insulation testing but only on a small number of...
Replies
4
Views
377

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top