Getting really low insulation res. readings from my D.B.
Neutral bar to Earth bar 0.35 M.O
Line & Neutral to earth 0.35 M.O

So strange, R.C.D. DOES NOT TRIP!

Have tried removing main earth and this makes no difference

If any 1 could shed any light be great

Cheers.
 
Firstly reconnect the earth immediately.

Can you give more detail on where and how you were doing the test and what tester and settings your using.

Does the RCD trip if you press the test button?
 
Using a megger on 250v & 500v. Found one fault, when i disconnected the pond pump the reading has now gone upto 1.2 M.O. and have narrowed this second low reading down to the ring main between neutral and earth.
 
Ah O.K. cheers whats the formula you used here?[/QUOTE]

No idea divided by several volts and adding 3 ohms over 2 amps............that should at least maim someone eh !! fgs?
 
Hardly strange, given that you have a resistance of 350,000 Ohms.

Therefore less than 0.0007A will flow. The RCD needs nominally 0.03A

Slow down Risteard your getting to far ahead of the class
[ElectriciansForums.net] Insulation resistance
 
Yep, the fault is too small to trip the RCD but I'd repair any fault under 1Mohm as a matter of course. If the fault has bee localised to a cble between 2 sockets then the cable may have been damaged or possibly there's damp in the sockets.
 
So when you do an insulation res. test before fitting an R.C.D. what minimum value would you be looking for?

Also would this now suggest my pond pump is on its way out or letting water in?
 
Surely with the 2391 under your belt this is stuff you should know !

So when you do an insulation res. test before fitting an R.C.D. what minimum value would you be looking for?

Also would this now suggest my pond pump is on its way out or letting water in?
 
So when you do an insulation res. test before fitting an R.C.D. what minimum value would you be looking for?

Also would this now suggest my pond pump is on its way out or letting water in?

a reading over 1Meg. is acceptable, but it's good practice to investigate anything under 2 Meg. the pond pump could just be moisture in an adaptable box or outdoor socket.
 
Surely with the 2391 under your belt this is stuff you should know !

Yeah i know that of course. But if you add an RCD you are making the safety alot better you can't be held liable for a fault already in place. You could advise the customer and charge to correct it, surely?
 
a reading over 1Meg. is acceptable, but it's good practice to investigate anything under 2 Meg. the pond pump could just be moisture in an adaptable box or outdoor socket.

Yeah cheers, there is no adaptable box, i checked the socket. Insulation res. went up when i pulled the plug to the pump.
 
Yeah i know that of course. But if you add an RCD you are making the safety alot better you can't be held liable for a fault already in place. You could advise the customer and charge to correct it, surely?

before adding an RCD you should test to see if there are any faults that will cause problems, along with earthing and bonding. you then factor the cost of fixing these faults as part of your quote.
 
Any pumps but especially submersible types are prone to low insulation. Even slight wear on the shaft or seal coupled with the heating and cooling during normal operation and it's all over for the IR. If it's a small domestic pond pump then it's probably better to replace with new rather than attempt repairs.
 
Hot motor /cold motor............summer /winter ambient temp lol.
Appliances just switched off or been standing for several hours.

The inexperienced will see faults that aren't there if their comparing results from previous tests:)
 
Doing an IR test with loads still connected is always going to end in tears.

Yeah i thought the load was removed so you don't fire 500v down your line and neutral and destroy items. Didn't realise, to be honest that items not in use but still plugged in would also still be a problem.
 
Instead of disconnecting the main earth to the board,try disconnecting the L N E of the circuit you are working on and test them,it's just possible that even though you have disconnected the main earth that the bonds to gas and water may be affecting your readings.
 

Reply to Insulation resistance in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Check the clearance between the back panel and/or terminal cover that you've removed. Look for small burn marks.
Replies
3
Views
378
  • Question
I may have been mistaken regarding TT I will look into that, thank you for the valued reply, but in general I stick to my post, a good topic for...
Replies
24
Views
3K
  • Question
There can be a few reasons for low L+N -> E readings: Connected equipment is leaking. By design, or just old/damp SPD are connected (but there...
Replies
9
Views
1K
When working in the motor repairs industry you have to fill in test sheets and keep them for so long. Doing that will do is ok for most things but...
Replies
10
Views
3K
  • Question
He is after the four options for 1 and 2 of the multiple choice exam, probably optimistic someone will know this. Your question 3 in incomplete to...
Replies
2
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks