Surely with the 2391 under your belt this is stuff you should know !

Yeah i know that of course. But if you add an RCD you are making the safety alot better you can't be held liable for a fault already in place. You could advise the customer and charge to correct it, surely?
 
a reading over 1Meg. is acceptable, but it's good practice to investigate anything under 2 Meg. the pond pump could just be moisture in an adaptable box or outdoor socket.

Yeah cheers, there is no adaptable box, i checked the socket. Insulation res. went up when i pulled the plug to the pump.
 
Yeah i know that of course. But if you add an RCD you are making the safety alot better you can't be held liable for a fault already in place. You could advise the customer and charge to correct it, surely?

before adding an RCD you should test to see if there are any faults that will cause problems, along with earthing and bonding. you then factor the cost of fixing these faults as part of your quote.
 
Any pumps but especially submersible types are prone to low insulation. Even slight wear on the shaft or seal coupled with the heating and cooling during normal operation and it's all over for the IR. If it's a small domestic pond pump then it's probably better to replace with new rather than attempt repairs.
 
Hot motor /cold motor............summer /winter ambient temp lol.
Appliances just switched off or been standing for several hours.

The inexperienced will see faults that aren't there if their comparing results from previous tests:)
 
Doing an IR test with loads still connected is always going to end in tears.

Yeah i thought the load was removed so you don't fire 500v down your line and neutral and destroy items. Didn't realise, to be honest that items not in use but still plugged in would also still be a problem.
 
Instead of disconnecting the main earth to the board,try disconnecting the L N E of the circuit you are working on and test them,it's just possible that even though you have disconnected the main earth that the bonds to gas and water may be affecting your readings.
 
O.k. forgot in 1 bed room there was surge protector under the bed, removed this and instantly gained from 0.36 to 1.6 M.O. Also found that unplugging my monitor for my mac gained another 1 meg to total 2.6 M.O. I'm happy for now with that, guess the rest could be the dishwasher or washing machine.
Again would this imply monitor or lead on way out?
 
a lot of electronic gear has earth leakage. always disconnect before testing. as cpl. jones famously said " they don't like it up'em".
 
a lot of electronic gear has earth leakage. always disconnect before testing. as cpl. jones famously said " they don't like it up'em".

So as long as the cause of low insulation r. is not the cable insulation, then it doesn't matter if the insulation reading drops right down to 0.1M.O. The reason has been investigated and would still be acceptable of course then?

I take it some items of equipment are more prone to leakage than others then
 
What you've discovered is that the earth is functional as well as protective. Depending what test voltage you use to mega test all surge arrestors will show as low insulation.
 
What you've discovered is that the earth is functional as well as protective. Depending what test voltage you use to mega test all surge arrestors will show as low insulation.

Now you mention it at 250v reading was 0.9 Mohm and 500v it read 0.36 if i remember correctly.
 

Reply to Insulation resistance in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
561
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
998
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
935

Similar threads

Thanks, I was hoping someone could confirm whether it was odd or not. I've done a fair bit of insulation testing but only on a small number of...
Replies
4
Views
377
Check the clearance between the back panel and/or terminal cover that you've removed. Look for small burn marks.
Replies
3
Views
619

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top