I was just doing an IR test on a ring and am a bit stuck, could one of you kind sir's please help me out?

I tested L-E got 20.4 MOhms
I tested N-E got 17.6 MOhms
I then tested L-N and got 0.00 MOhms

Anybody got any ideas why I would gave 0.00 MOhms when testing L-N?

Many Thanks
Mark
 
Often missed Heating spurs, hidden kitchen sockets and spurs and the one most forget is the mains powered igniter on a gas cooker.
 
I took a customers kitchen apart today for a CU swap as all the sockets where behind built in applliances.

And he thought i was going to put it all back!!!! :D:D:D:D
 
Is this for a periodic, minor works, or installation, just out of interest?

Edit - if it's a periodic then it is acceptable to connect all live conductors (i.e. lines and neutrals) together and just test to the protective earth...
 
Last edited:
Chaps

I was just doing an IR test on a ring and am a bit stuck, could one of you kind sir's please help me out?

I tested L-E got 20.4 MOhms
I tested N-E got 17.6 MOhms
I then tested L-N and got 0.00 MOhms

Anybody got any ideas why I would gave 0.00 MOhms when testing L-N?

Many Thanks
Mark
Hi
You are Lucky i get 0.00 on all three are you using Kewtech KT61

Thanks

Mark
 

Reply to Insulation Resistance in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
485
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
956
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
900

Similar threads

If the main switch is on when testing global IR then the neutral and earth will likely give a very low reading. Not that anyone would...
Replies
10
Views
680
loz2754
L
Continuity of the suspect cable appears fine all cores, from this I could work out the length of it and it really doesn’t appear looking at the...
Replies
2
Views
418

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top