Hello to you all, and apologies for another question on this topic but I'm new to all this and completely stuck!
I've been testing a Ring Final circuit today with a Megger MFT and got a bizarre reading on one of the IR tests.

On the continuity test I seemingly got correct readings on all the tests, however I never tested Neutral to CPC at the time.

Then when I came to do the IR test on the ring everything was proceeding as planned until I tested Neutral and CPC. The meter just reads 0, not even a smidgen of a reading, am I right in assuming that there is a short between neutral and cpc?

When I then went to find the problem using a continuity test with outgoing Neutral and incoming CPC connected together and vice versa, I gradually get smaller readings towards one section of the ring, so is this where the problem is located?

I also noticed that in most of the sockets, I didn't need to turn the socket on to get my continuity readings whereas I'm sure I did for the Live/Cpc tests, is this indicative of the fault also.

Thanks so much for your assistance, apologies for asking and look forward to your replies:)

Alan
 
Then when I came to do the IR test on the ring everything was proceeding as planned until I tested Neutral and CPC. The meter just reads 0, not even a smidgen of a reading, am I right in assuming that there is a short between neutral and cpc?



Almost certainly.

When I then went to find the problem using a continuity test with outgoing Neutral and incoming CPC connected together and vice versa, I gradually get smaller readings towards one section of the ring, so is this where the problem is located?



Probably not. Ring resistance will vary around ring, max furthest away from CU.


I also noticed that in most of the sockets, I didn't need to turn the socket on to get my continuity readings whereas I'm sure I did for the Live/Cpc tests, is this indicative of the fault also
.

Probably not. Could have mix of single and double pole sockets.


Most likely you clipped neutral cable against back box or with screw whaen attaching socket cover.

Divide ring into 2. IR test both halves (like a radial) one will fail this is half fault is on.
\Keep dividing down til identify fault location.
 
You shouldnt need to switch any of the sockets on to get a continuity reading on a ring? They loop in then back out, without going through the switch.
 
Thank you so much for replying guys, especially MikeK, your help is most appreciated. :)

Managed to sort it out today, took a while but got there in the end, biggest problem was It was in an old house and I never wired the ring so I was unsure where the next socket on the ring was!

But all sorted now thanks!

P.s. I was using a socket adaptor with the Megger, thanks for checking though:D
 
Hi, i found 2 faults on the ring.

In one of the sockets whoever stripped the cable back had obviously used a Stanley blade and slit the neutral insulation right up to the box entry (there was a grommet btw:)). The other fault was between two sockets but I've no idea what it is, I just split the ring in 2 and made two radials on 20A MCB's.

Must be a fault buried under the floor or in the wall as the cables into the box looked fine.

Thanks again for your assistance, very much appreciated:D
 

Reply to Insulation Test Problem (sorry!) in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
344
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
882
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Continuity of the suspect cable appears fine all cores, from this I could work out the length of it and it really doesn’t appear looking at the...
Replies
2
Views
334
If the main switch is on when testing global IR then the neutral and earth will likely give a very low reading. Not that anyone would...
Replies
10
Views
601
loz2754
L

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top