SolarJuice
Hi ladies and gents, my first post.
Can anyone clarify a few things?
Can the PME earth (TNC-s) earth provided by the dno be extended out into a field? lets say for a solar farm of just 50kW? I have been informed that it can by a representitive from ELECSA but I was always under the impression that the armour earth should be terminated at the far end and an earth e;lectrode installed to convert the far end installation to TT system, I have been with NICEIC for years, (ensuring labelling in place and that the 2 earths could not be simultainiously touched)
Also can anyone tell me the largest size of service head/cut out fuse provided by the DNO? I have only ever been familiar with 100A 3 phase. Therefore plans for a new PV installation above 50kW (>74 ish Amps per phase) would require discussions around the transformer size on site/nearby?
Have any of you got suggestions for books or short courses on introduction to HV?
Thanks guys!
Can anyone clarify a few things?
Can the PME earth (TNC-s) earth provided by the dno be extended out into a field? lets say for a solar farm of just 50kW? I have been informed that it can by a representitive from ELECSA but I was always under the impression that the armour earth should be terminated at the far end and an earth e;lectrode installed to convert the far end installation to TT system, I have been with NICEIC for years, (ensuring labelling in place and that the 2 earths could not be simultainiously touched)
Also can anyone tell me the largest size of service head/cut out fuse provided by the DNO? I have only ever been familiar with 100A 3 phase. Therefore plans for a new PV installation above 50kW (>74 ish Amps per phase) would require discussions around the transformer size on site/nearby?
Have any of you got suggestions for books or short courses on introduction to HV?
Thanks guys!