Hi,

I have an aico alarm system which was mains powered and interconnected when installed 3 years ago. It's not been maintained and when I took a look recently, a couple of the detectors are missing. Only the ceiling plate is on the ceiling. Also, the interconnect isn't working. When I test any smoke detector, only that beeps and - none of the others.

I need to ensure that they are all still mains powered and restore the interconnection between them. They have a 3 core and earth cable for the interconnect.

I am pretty handy with electrics and own various tools including a fluke 2 pole tester.

I have 8 detectors. Can you please suggest a logical approach for this. Does the indicator on the detectors have any significance?

Look forward to receiving your advice. Thanks in advance.
 
Missing heads shouldn't have any impact on hardwired interconnection as remaining heads will still communicate with each other.

They should and should be relatively straightforward to establish what's going on here

I'd tend toward removing all heads first and work from there , sort out the interconnect and get 2 heads fully operational
 
They should and should be relatively straightforward to establish what's going on here

I'd tend toward removing all heads first and work from there , sort out the interconnect and get 2 heads fully operational

Assuming the system is correctly wired and originally worked, what issues might occur beyond connections in each base or damage to fixed wiring?
 
I'd be very cautious about working on the wiring with heads in place after i blew all the heads in an installation once

I wouldnt be totally amazed if the interconnect isn't working on the heads either although it's much more likely to be the wiring
 
Assuming the system is correctly wired and originally worked, what issues might occur beyond connections in each base or damage to fixed wiring?

Assuming the system is correctly wired and originally worked, what issues might occur beyond connections in each base or damage to fixed wiring?
I suppose that's what I was wondering did the interconnect originally work

I blew all the EI/aico alarms in a new installation once, foolishly mixing supply and interconnect

Another time I saw an installation with where the interconnect didn't work at all and the supply /interconnect was looped from one to the next, so I would expect it to be operational to some extent

So I was keeping an open mind on this
 
Good reason not to use T&E for the interconnect, Aico recommend min 0.75mm perhaps boot-laced multi strand would be preferable, personally I have not used cable interconnect preferring the radio link, much easier.
 
UPDATE: I finally got around to taking a look at this today and wanted to share my finings and plead for further help please.

  • Firstly, none of them had the green or red light on display
  • Some of the detectors beeped upon using the test button and some did not. None of them caused other alarms to beep at the same time.
  • I then removed the heads and started testing across live and neutral using my 2 pole tester. None of them had mains power
  • I noticed that all of them had 2 sets of 3 core and earth cables - except one which had 3 sets of 3 core and earth and another alarm that had 1 set of 3 core and earth and 1 set of 2 core and earth.
  • That last detector was the power supply and again, had no power when tested with the 2 pole tester
  • I then traced this cable in the loft and quickly found a Fused Spur that was switched off! I have now marked this appropriately
  • [ElectriciansForums.net] Interconnected smoke alarm - troubleshooting
  • Once this was switched on, all base units had power
  • I slid the heads back in and they all had the green light apart from two
  • [ElectriciansForums.net] Interconnected smoke alarm - troubleshooting
  • these two heads were unlit when tested in other bases too. I concluded that they were faulty and needed replacing

However, none of the alarms are causing any of the others to beep. I tested each one individually and held down the test button for over 10 seconds. Only that alarm beeped. They've all got an interconnect cable and the same colour is being use throughout and this system was working when first installed a few years ago.
[ElectriciansForums.net] Interconnected smoke alarm - troubleshooting


All the heads are Ei141rc apart from the kitchen heat sensor. This is EI144RC.
[ElectriciansForums.net] Interconnected smoke alarm - troubleshooting

[ElectriciansForums.net] Interconnected smoke alarm - troubleshooting

1 of the EI141RC has this sticker and if I recall correctly was installed more recently. Still the same model as the others?

And here is the heat detector in the kitchen:
[ElectriciansForums.net] Interconnected smoke alarm - troubleshooting


I am at a a loss and hoping that you can shed some light on this. Thanks again.
 
From the manual available here: Ei144RC Instructions - Aico - https://www.aico.co.uk/downloads/ei144rc-instructions/

"Interconnected Alarms only - Test the first unit by pressing the button for 10 seconds. All the units should alarm within 10 seconds of the first horn sounding. The red light on the first unit only will flash about once a second. On releasing the button the local Alarm will stop sounding immediately and the remote Alarms will stop sounding approximately 3 seconds later (if testing using RF interconnection this could take slightly longer). This will verify that the interconnect is working. Check all the other units similarly."

If this does not work then suspect continuity issues with the interconnect as suggested above.
 
You need to carry out some continuity tests to verify all conductors.
Can you elaborate on this please. Not a trade leccy!
Do you mean continuity on the interconnect cable? Even if a few of the links were broken (which I have no reason to believe) I expected the remaining devices to work in tandem. It would be very unlikely that all of them have broken interconnects?

Note that mains power is carried across to all the devices.
 

Reply to Interconnected smoke alarm - troubleshooting in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
380
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
957
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
That explanation would make a lot of sense and would certainly explain the new bases and new boxes, with old relabelled alarm heads. I do remember...
Replies
5
Views
735
  • Question
Personally I won't do fixed price work unless there is a clear spec for the job including things like smokes, data, TV whatever else the customer...
Replies
3
Views
787

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top