Hi,

I have an aico alarm system which was mains powered and interconnected when installed 3 years ago. It's not been maintained and when I took a look recently, a couple of the detectors are missing. Only the ceiling plate is on the ceiling. Also, the interconnect isn't working. When I test any smoke detector, only that beeps and - none of the others.

I need to ensure that they are all still mains powered and restore the interconnection between them. They have a 3 core and earth cable for the interconnect.

I am pretty handy with electrics and own various tools including a fluke 2 pole tester.

I have 8 detectors. Can you please suggest a logical approach for this. Does the indicator on the detectors have any significance?

Look forward to receiving your advice. Thanks in advance.
 
In terms of testing the cabling there are two separate tests that need doing :

1) Check that (with all the heads removed) there is no connection between any of the four wires (including earth). If (say) the interconnect was shorted to the neutral then the interconnect wouldn't work and you'll get the symptoms described (only the one unit will sound).

2) Check that there's a complete link along each - i.e. L, N, and interconnect is connected between all the bases. As already said, if there's a break in the interconnect then the units will work in separate groups - those one side of the break, and separately the ones the other side of the break.

And for this size on installation, there really should be a test/isolate switch which for a hardwires system would be the one littlespark posted a photo of in post #76.
 
As an observation rental properties should not have battery backed ionisation alarms fitted , should be optical with built in rechargable battery ie:3016 from AICO , this applies in hallways and general living spaces , heat alarm in the kitchen , ionisation are acceptable in bedrooms.
 
As an observation rental properties should not have battery backed ionisation alarms fitted , should be optical with built in rechargable battery ie:3016 from AICO , this applies in hallways and general living spaces , heat alarm in the kitchen , ionisation are acceptable in bedrooms.
Where does it state this? I was advised by the local authority to fit a mains powered interconnected system. There was no additional stipulation.
Can you clarify please.
 
Wouldn't surprise me if he's also right on the requirement for mains +rechargeable

That's the way it should be for rented accommodation, as near as possible to a maintenance free system

So what the council are now requiring here(Eire) when leasing property for rental is a fire panel fitted , seems like overkill but...
 
This is from the Aico electrical contractors handbook
 

Attachments

  • 426DBB5C-4E82-492B-B936-80AE8C998208.jpeg
    426DBB5C-4E82-492B-B936-80AE8C998208.jpeg
    389.9 KB · Views: 49
  • 1E38561F-40F4-45ED-9CB3-25F762B3C996.jpeg
    1E38561F-40F4-45ED-9CB3-25F762B3C996.jpeg
    374.7 KB · Views: 54
So "recommended", not "mandatory". But I'd not user user-replacable batteries anyhow - to tenants they are either a nuisance that can be silenced by removing the battery, or a handy spare battery for something else ?
Can you silence them by removing the battery alone , don't think so ?

What they will do is slide off the whole lot and take out the battery
 
Aico 141 and 146 smoke alarms will be silenced if you remove them from their base. This disconnects both the mains supply and the battery.
If the alarm is refitted without the battery it will still do what it's designed for, but will emit an annoying single bleep every couple of minutes, the same as with a failing battery.
Most common cause of removed Aico 146 alarms is false sounding because of dust in the optical chamber.
 
Aico 141 and 146 smoke alarms will be silenced if you remove them from their base. This disconnects both the mains supply and the battery.
If the alarm is refitted without the battery it will still do what it's designed for, but will emit an annoying single bleep every couple of minutes, the same as with a failing battery.
Most common cause of removed Aico 146 alarms is false sounding because of dust in the optical chamber
They're supplied with battery connected ,so stands to reason you can just whip off the head to silence it , if im getting it right

Was assuming first you'd also have to remove alkaline battery, I should probably remember
 
UPDATE: I created a test rig with two new smoke alarms. I connected them together using 3 core and earth - on the ground (powered by 9v battery) and as expected, the interconnect works with them. I then removed one of the new heads from this set-up and replaced it with each of the 8 heads currently in the house. I tested each of them in both directions: tested the new alarm and the head from the house. None of them apart from one provided the interconnect. They all worked independently. I concluded that 7 of the detectors were faulty.

I purchased 7 new alarms, popped them on one device after the other whilst testing them. They all work!
I did inspect the wiring on each detector and it seemed fine.

I did notice that one of the bases had a burn mark. I replaced this base but with all other detectors, I retained the old bases and slid on the new heads.


All the faulty detectors had a "Replace By" date of June 2026.


I have written to Aico to see if they can cover any of the cost but unfortunately, I don't have receipts for the old detectors.

Here are some images of the call point:

I am questioning whether there is any benefit in having a key for this as it's just as easy to test the system from any of the detectors.

Interested in your thoughts on the above and also, what may have caused the issue which led to all the interconnects failing. Since I have not changed anything other than fitting the new heads, could the underlying issue still be there? Also, is there any reason to retain or fit the bases that came with the new detectors? I left the old bases apart from the one that had a burn mark.

Can I also take this opportunity to thanks everyone for their help and advice.
 

Attachments

  • 1636232689286.png
    1636232689286.png
    625.3 KB · Views: 47
  • 1636232799819.png
    1636232799819.png
    502.7 KB · Views: 46
  • 1636232799087.png
    1636232799087.png
    1.3 MB · Views: 44
  • 1636232894012.png
    1636232894012.png
    745.8 KB · Views: 45
  • 1636232894423.png
    1636232894423.png
    502.7 KB · Views: 45
  • 1636232894895.png
    1636232894895.png
    1.1 MB · Views: 37
  • 1636232947037.png
    1636232947037.png
    552 KB · Views: 45
  • 1636232946811.png
    1636232946811.png
    502.7 KB · Views: 34
  • 1636232946445.png
    1636232946445.png
    1 MB · Views: 42
  • 1636232947356.png
    1636232947356.png
    1.1 MB · Views: 46
  • 1636232987222.png
    1636232987222.png
    502.7 KB · Views: 45
  • 1636232987416.png
    1636232987416.png
    552 KB · Views: 43
  • 1636232987874.png
    1636232987874.png
    787.2 KB · Views: 42
  • 1636232988294.png
    1636232988294.png
    1.1 MB · Views: 43
  • 1636232986708.png
    1636232986708.png
    1.6 MB · Views: 44
On a system that size you really need a test switch - otherwise if there's an alarm, you'll be chasing round trying to find the one that's triggered, while being deafened by the racket. With the test switch, you can press the locate switch and all but the one that triggered will turn off.

And of course, if it's rented then tenants (even ones you thought were good ones) will be quite ready to remove what they consider to be "faulty" alarm heads. And since they probably aren't familiar with the little details, they might not use the slot to release the slide lock - so next time you do an inspection you find that the base is broken as well as the head missing. Guess how I know that ?
 
On a system that size you really need a test switch - otherwise if there's an alarm, you'll be chasing round trying to find the one that's triggered, while being deafened by the racket. With the test switch, you can press the locate switch and all but the one that triggered will turn off.

And of course, if it's rented then tenants (even ones you thought were good ones) will be quite ready to remove what they consider to be "faulty" alarm heads. And since they probably aren't familiar with the little details, they might not use the slot to release the slide lock - so next time you do an inspection you find that the base is broken as well as the head missing. Guess how I know that ?


I’m pritty sure the locate function only works if it is a rf system
 
You can mix and match with the Aico stuff. In our rental flat we have one sensor and the switch wired, two more sensors wired, and radio modules in two sensors to bridge the two wired segments.
Operting the test switch makes its hardwired head sound immediately - then a couple of seconds later the other two heads sound.

What you don't get on a wired setup (but do with radio) is having all the sensors sound according to the function that triggered. E.g. a Heat & CO head will make different sounds depending on what triggered it. In a radio linked setup, all the other heads will copy that. But with wired interlink they just do their default sound.
 
Intrigued to hear about possible causes for the IC failure on all but 1 of the detectors. Also, the new detectors are on the same wiring and currently working.
Not really following the thread but I've seen interconnect failure a couple of times

Caused it once myself by crossing the wiring and blew the heads , lesson learned

Have also seen it in an installation i was working in, wired but not working
 
Near the beginning of this thread is a pic of the wiring to a head, showing that the wiring colour conventionally used for the interconnect and the neutral have been swapped around. I suspect that at some point a damaged base has been replaced by an electrician who connected the new one conventionally before realising his mistake after powering up. Corrected his wiring, and then walked swiftly away.
 
Intrigued to hear about possible causes for the IC failure on all but 1 of the detectors. Also, the new detectors are on the same wiring and currently working.

Has someone been in and performed an insulation resistance test on them at 500V?
 
Near the beginning of this thread is a pic of the wiring to a head, showing that the wiring colour conventionally used for the interconnect and the neutral have been swapped around. I suspect that at some point a damaged base has been replaced by an electrician who connected the new one conventionally before realising his mistake after powering up. Corrected his wiring, and then walked swiftly away.
This one ?
It strikes me that there's an indication of sub-standard design in these then. Given that such wiring errors are not exactly unforeseeable, you'd think they'd design the system to cope with it - it is possible to do.
 
This one ?

It strikes me that there's an indication of sub-standard design in these then. Given that such wiring errors are not exactly unforeseeable, you'd think they'd design the system to cope with it - it is possible to do.
You mean design the heads to cope with wiring errors ?

Is this a common issue or does it occur with other brands.Think it was EI in both cases I seen
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
United Kingdom
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
DIY or Homeowner (Perhaps seeking pro advice, or an electrician)

Thread Information

Title
Interconnected smoke alarm - troubleshooting
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
111
Unsolved
--

Advert

Thread statistics

Created
Neptune,
Last reply from
Mikegh,
Replies
111
Views
17,612

Advert

Back
Top