HV,LV whats MV? thought MV was old hat.What factors determine the interconnection of the MV neutral/earth with the LV neutral at the local substation? When are they connected together and when would it be appropriate not to connect them together?
NopeHV,LV whats MV? thought MV was old hat.
wheres does MV Start and HV kick in? and where does it state the parameters ?Nope
ELV, LV, MV, HV, EHV etc all still very well defined.
it is only the wiring regs that simplifies everything above LV as "HV"
I thought MV was 1-33kVwheres does MV Start and HV kick in? and where does it state the parameters ?
Iec 60071 defines MV as 1kV to 36kVwheres does MV Start and HV kick in? and where does it state the parameters ?
Oops, yes 275, got mixed up with some other work - must pay better attention.Most power distibution is at 132kv (highest voltage for a DNO), 275kv and 400kv. I've never seen or heard of 232kv.
At EHV you don't have to worry about touching a live conductor. You would be dead well before you touched anything. NG safety distances are 1.4m at 132kv, 2.4m at 275 and 3.1m at 400kv but in reality it's 'as far away as f'in possible'.I'm assuming they are phase-neutral (i.e. earth) since the main risk of shock is touching a line conductor while in contact with the Earth (or attached parts)
A reasonably quick way to tell the voltage of a pylon. If it's just got 1 cable per phase it's 132kv. 2 cables is 275kv and 3 or 4 is 400kv.Most power distibution is at 132kv (highest voltage for a DNO), 275kv and 400kv. I've never seen or heard of 232kv.
And next comes UHV.Iec 60071 defines MV as 1kV to 36kV
Most others take the value as 35kV (such as iec60038)
HV is 35kV to 230kV
EHV >230kV
Unless you're not on the ground...At EHV you don't have to worry about touching a live conductor. You would be dead well before you touched anything.
Interesting stuff,
I thought HV power distribution was delta, so no neutral (star point)
I have no basis for this, other than my own conclusion from looking at 3 wire overhead lines, going to what i presumed were delta to star transformers to step voltage down to 230v (415v) and provide a neutral / earth for consumers??
Nope, the same, I have had little to do with transmission stuff in a practical sense.I wouldn't do that job for any money! I wouldn't climb the pylons either. I'm happy when I'm just climbing about all over the transformers ?
LV networks are always solidly earthed and may be TT TNS or TNC-S.Does the grounding at the HV-MV substation play any role? I've heard that MV systems in the UK are resistance or peterson coil earthed. Is this true?
Protection as in relays or on TX protection like Bucholz, PRV's WTI/OTIs etc?Only been involved in the protection side of it, so far far away...
Relay, at one (two) time I worked for a couple of protection equipment manufacturers and their associated consultants.Protection as in relays or on TX protection like Bucholz, PRV's WTI/OTIs etc?
On the relays eh? So you're on the high paid jobs and the nice warm/ air con switchrooms tapping keys on a laptop while us real workers are crawling all over the transformers getting soaked in transformer oil with the rain running down the necks of our overalls ? Okay, we do spend time in the switchrooms too, doing the maintenance/timing tests etc. on the breakers. We normally use our own guys for protection or if we are fully booked then we call in guys from Oberon Engineering.
I had wondered about this with the small (0.5MVA) substation that feeds our stuff. The map of buried cables shows it fed from an 11kV 95mm 3-core aluminium cable.The main distribution voltage is 11kV although other voltages are used. The 11kV network can be solidly earthed or resistance earthed through liquid or dry resistors.
Not locally, no.I had wondered about this with the small (0.5MVA) substation that feeds our stuff. The map of buried cables shows it fed from an 11kV 95mm 3-core aluminium cable.
I had always assumed it would be a simple delta-star transformer with just the star point of the LV (230V) side earthed and the HV side earthed at the source end, but is it likely to have an HV side earthing transformer as well?
I mean each rod was 10-15 ohms.However, it is an area of good soil conductivity, as I got around 10-15 ohms for a couple ord 2m x 16mm rods driven in to the forever damp clay soil there