Street lighting circuits would never comply if that wasnt the case.
Well you have 2 options:
It's up to you which one you choose, but I would go for the second option.
- Wire the cct as a FLC
- Do it properly.
That's my thought on the matter, take it or leave it.
IMO it relates more commonly to the reduction in CSA of a pendant wired in 0.5mm flex from a 1mm or 1.5mm lighting circuit, but either way in this situation there should be a protective device at the reduction in CSA where the ring 'lollypops' off, making the SWA a submain. The ring would then begin at this point, in line with convention.I suppose by the letter of the regs you should as your reduction in CSA will exceed 3 metres, but has the protection is just 32amps for the entire circuit and your using 6mm radial and 4mm for the RFC then I would only be fitting the one OPD at the origin.
Reg 434.2.1 IMO is aimed a circuit where you have a 63amp Ring Main in 10mm and you want to tap off for <3 metre in say a 6mm for something.
Read what you entitled the thread.Read post #25!!!
Funnily enough, I really don't need you telling me how to ''Do it properly''.
IMO it relates more commonly to the reduction in CSA of a pendant wired in 0.5mm flex from a 1mm or 1.5mm lighting circuit, but either way in this situation there should be a protective device at the reduction in CSA where the ring 'lollypops' off, making the SWA a submain. The ring would then begin at this point, in line with convention.
IMO it relates more commonly to the reduction in CSA of a pendant wired in 0.5mm flex from a 1mm or 1.5mm lighting circuit, but either way in this situation there should be a protective device at the reduction in CSA where the ring 'lollypops' off, making the SWA a submain. The ring would then begin at this point, in line with convention.
If there is a protective device where the SWA joins the ring the protective device at the origin could be something other than a 32A RCBO. Alternatively maybe a different installation method could be used to make the circuit an ordinary ring; I don't know, I don't like to ask.What would you suggest as a protective device at the point where the radial becomes a ring?....given that there is a 32a RCBO at the origin,in order to provide discrimination a 20a device would be required at the point of change according to your view...note change,not reduction..as both the SWA and ring meet the requirements for a 32a OCPD the change surely cant be classed as a reduction?
Well do that then. I don't like the idea of a lollypop circuit, but then it's not me doing the job.In simple terms now ....Rubbish!! Lollipop rings have been around for years now. Providing protective measures are fulfilled along with any other circuit parameters then they are electrically sound and will comply....
If there is a protective device where the SWA joins the ring the protective device at the origin could be something other than a 32A RCBO. Alternatively maybe a different installation method could be used to make the circuit an ordinary ring; I don't know, I don't like to ask.
I read your post #25 and it didn't explain why you 'have to' install the circuit like this, not that I should bother reading your posts when you can't even be bothered to explain your ambiguous initialisms.You don't have to Ask, ...that question has been answered in my Post #25, that i believe i directed you too previously...
I read your post #25 and it didn't explain why you 'have to' install the circuit like this,
Like I've already said you can either install a lollypop circuit or not.
The Lollipop Circuit
In my design ill assume that at the far end of the circuit there is a 20 amp load and an additional 12 evenly distributed around the circuit, average current = 32 + 20/2 = 26 amps.Providing load current in any part does not exceed 26amps we may use an Iz of the below.
Iz Equal > 26 amp, 6mm, 2.5 so both are o.k
Volt drop = Distribution Circuit 10 meters 6mm, Ring/Parallel circuit 60 meters
Radial = 2.336 volts Ring equals = 7.02 volts = 9.356 volts so less tan the 11.5
Fault Protection Maz Zs(32 Amp type B) = 1.44 Ohms Ze = .35 Ohms(TNC-S) 100 amp 1361 type II
Distribution Circuit = .13 Ohms Ring = .35 Ohms = ZS = .83 So comply's
Fault current Protection Front end using adiabatic and energy let throughs Minimum size = . 38mm
far end minimum size .21mm so comply's
Short circuit Front end .38mm Far end = .30mm so comply's32 Type b 60898, fusing factor 1.45 = Must trip within 1 hour at 46.4 amps
If i place a 46.4 load between the two legs at the mid point of a ring the load will be split between the two legs.
So we know it will trip within 1 hour at that load and the split load will equal 23.2 amps per leg, now 2.5 is 27 amps.
Is the cable protected yes.
The key is even distribution of load.
Now common sense tells us that if i place some 6mm in front of this ring it not going to have a major impact on the current distribution of the circuit.
Omit overload Protection at JB Using 433.3.1
Utilizing Appendix ten and using kirchoff's law to evaluate the load in each section, it can be seen that the cable is protected.
434.2.1
"The part of the conductor between the point of reduction of CSA or other change and the position of the protective device shall... ... not exceed 3m in length..."
Does that help?
ie are you fusing it down after the SWA, or could you just use, say, a 4mm radial throughout?