Is the RCBO single pole(SP) OR single pole with switched neutral(SPSN)? To find out out which, isolate the RCBO and measure continuity between Nin and Nout when RCBO open and then closed. (There is a circuit capacitance effect which can be troublesome to residual current detectors when a switched neutral conductor is first energised (at a similar(but not absolutely identical) moment to the switched line conductor becoming energised).
Have you done standard FRC checks ? What where the result ? Of particular interest are the figure of 8 readings at each socket taken in step from the first socket on the 'outward leg' and ending on the first on the 'home leg'. As well as the L-N and L-E figure of 8 also do an N-E figure of 8 set of tests. (This is to explore whether the ring is symmetrical to currents flowing clockwise and anti-clockwise or if there is in fact a direction around the ring with a lower conductance path for the line currents which is opposite to the direction of lower conductance path for the neutral currents). Or in other words, the currents at the beginning of a leg should equal eg: 10A/10A and 20A/20A not 10A/15A and 20A/15A.
That occurrence,may need further explaining...