I was called out to look at an RCBO tripping that powers a ring final circuit in a youth cafe.
Checked the IR values at the DB - and all >299. I removed the conductors from the RCBO and checked just that circuit.
Now weirdly, when I go to one of the sockets and test either way, the value for L-E is 0.12 when the conductors are back in at the DB end. To prove a point I then removed the conductors at the DB and stuck in some wago's, i.e. L-L, N-N and E-E. When testing at the socket again, >299.

Also checked the RCBO on its own, that seemed to function just fine.

Anybody got any ideas?
 
Suspect faulty appliance or something being plugged in. Generally the case. Id do Continuity tests. Difficult Without more detail i.e intermittent or permenant fault, when is it tripping etc..

Well I'd be sending the client round unplugging whilst I had a look round as well then unpack my megger and start with IR and cont, then Rcd testing first offload then onload as well.
That's after a chat with client to diagnose problems/symptoms which is usually the best course of action. I was told in college with fault finding the best way is to grill the client regarding the fault and what's been going on in the property drilling walls, new appliances etc otherwise you could be going round in circles. Found a faulty kettle once on the phone form 200miles away in 5minutes lol
 
Nothing plugged in, that was my suggestion on the phone when the client first rang me. Oh and yes neutral fly-lead + earth lead removed whilst testing.
With either side of the ring connected to the RCBO (in turn) will operate fine. When both all are connected, RCBO trips.
I had all the sockets off and removed the conductors from terminals and IR tested all conductors individually, all >299.
 
I was called out to look at an RCBO tripping that powers a ring final circuit in a youth cafe.
Checked the IR values at the DB - and all >299. I removed the conductors from the RCBO and checked just that circuit.
Now weirdly, when I go to one of the sockets and test either way, the value for L-E is 0.12 when the conductors are back in at the DB end. To prove a point I then removed the conductors at the DB and stuck in some wago's, i.e. L-L, N-N and E-E. When testing at the socket again, >299.

Also checked the RCBO on its own, that seemed to function just fine.

Anybody got any ideas?

Could you tell us:

Is the RCBO tripping upon being closed or randomly some time afterwards? Has the fault just started happening after a prolonged period of satisfactory state?

What types of equipment are connected to this RFC?

Could you clarify this figure by including the units please? eg: 0.12MOhms, or 0.12 Ohms or what?

What is the type of supply: TT, TNCS or TNS?

What is the make of RCBO. Do you know if it a basic type or electronic type?
 
Last edited:
Well I'd be sending the client round unplugging whilst I had a look round as well then unpack my megger and start with IR and cont, then Rcd testing first offload then onload as well.
That's after a chat with client to diagnose problems/symptoms which is usually the best course of action. I was told in college with fault finding the best way is to grill the client regarding the fault and what's been going on in the property drilling walls, new appliances etc otherwise you could be going round in circles. Found a faulty kettle once on the phone form 200miles away in 5minutes lol


Inspector Gadget?

[ElectriciansForums.net] Interesting problem
 
RCBO trips immediately after connecting both legs of the ring. Figures are 0.12MOhm. On a TNCS 3P Supply.
Oh and MEMshield 2 C Type RCBO.
 
RCBO trips immediately after connecting both legs of the ring. Figures are 0.12MOhm. On a TNCS 3P Supply.
Oh and MEMshield 2 C Type RCBO.

Is the RCBO single pole(SP) OR single pole with switched neutral(SPSN)? To find out out which, isolate the RCBO and measure continuity between Nin and Nout when RCBO open and then closed. (There is a circuit capacitance effect which can be troublesome to residual current detectors when a switched neutral conductor is first energised (at a similar(but not absolutely identical) moment to the switched line conductor becoming energised).

Have you done standard FRC checks ? What where the result ? Of particular interest are the figure of 8 readings at each socket taken in step from the first socket on the 'outward leg' and ending on the first on the 'home leg'. As well as the L-N and L-E figure of 8 also do an N-E figure of 8 set of tests. (This is to explore whether the ring is symmetrical to currents flowing clockwise and anti-clockwise or if there is in fact a direction around the ring with a lower conductance path for the line currents which is opposite to the direction of lower conductance path for the neutral currents). Or in other words, the currents at the beginning of a leg should equal eg: 10A/10A and 20A/20A not 10A/15A and 20A/15A.
 

Reply to Interesting problem in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
439
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
It is not that they don't trip, it is that putting a probe in the front of the RCBO to contact the terminal bypasses the sense coil so the RCBO...
Replies
7
Views
707
davesparks
D
Induced voltage can be a bit of a red herring when using DVM my guess is somethings moist.
Replies
5
Views
474
TerryBNZ
T

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top