I guess at least the plumber used 6mm

I have recently seen a brand new 8.5kw shower wired up in 1mm flex to a redundancy immersion switch Backed up by a 32a rewire fuse

Nice
 
Haha. As long as they complete their shower in 1.55 seconds then the cable won't overheat lol!

I wish I had taken a photo of it.
The 1mm comes out the switch , wraps round the cold feed pipe about 8 times then follows the pipe straight through the wall into the back of the shower

It truly is a work of art
 
Lol. Actually, I was messing around. It would take 357 seconds to overheat, (sq.rt 1sq x 115sq / 36.95 =)
The plumber has allowed for some extra time though by providing liquid cooling by wrapping around cold water pipe hahaha.

Edit: Jim, yes....you beat me too it. Clever chaps those plumbers! :)
 
Lol. Actually, I was messing around. It would take 357 seconds to overheat, (sq.rt 1sq x 115sq / 36.95 =)
The plumber has allowed for some extra time though by providing liquid cooling by wrapping around cold water pipe hahaha.

Edit: Jim, yes....you beat me too it. Clever chaps those plumbers! :)
It's dual purpose-pre-heats the cold feed too!
 

Reply to Interesting shower hook up in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
438
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Hi, i am wondering if anyone has any experience with a 7.5-8kw shower that has a pump or some sort of boost internally fitted? Working at a hotel...
Replies
0
Views
232
Depends how it is connected, which is of course a practical issue, the terminals are usually designed for 6/10mm cable so if you can ensure the...
Replies
3
Views
329

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top