timhoward

-
Broke Internet
Esteemed
Arms
Supporter
Joined
Jul 19, 2019
Messages
4,618
Solutions
1
Reaction score
9,847
Location
Oswestry
I'm doing testing ahead of a board change. It's a cramped Wylex rewirable installed by Spiderman himself. (I still haven't worked out why there seem to be 4 lives and 5 neutrals for lighting circuits, but that mystery will have to wait until the point of no return)
I eventually got the RFC lives and neutrals untangled and removed for an IR test. The cpc's are still connected unfortunately. L+N together to E at 250v is giving 8Mohms and slowly rising (reached 10 and still rising when I let go), but at 500v it's giving 0.5 Mohms.
Other than looking harder for connected equipment that I've missed is there anything this instantly suggests please?
I was suspecting outside lights on a FCU or something but can't see any.
(Zs is ok for all circuits. RFC continuity end to end is good too. Current main concern is this IR test result)
TIA
 
IR should be done with the CPCs connected to earth.

I'd double check for connected equipment, things like switched mode power supplies can really mess your readings up, so can extension leads with surge protectors.
 
That sort of thing is common for SPD in something like an extension block, etc, but usually more extreme than that.

It would bother me as well if I could not find a reason, as the point of 500V testing is to uncover weaknesses in cables!
 
As above the CPC should be connected for this sort of test.

But if you see something dodgy, which you do, then try doing the test again but L+N to isolated CPCs. If much better then it really is a fault from cable to something else somewhere (i.e. leak to building via damaged sheath, not via cable's own CPC to connected equipment).
 
As above the CPC should be connected for this sort of test.

But if you see something dodgy, which you do, then try doing the test again but L+N to isolated CPCs. If much better then it really is a fault from cable to something else somewhere (i.e. leak to building via damaged sheath, not via cable's own CPC to connected equipment).
Cheers, I did a mind jump - I meant unfortunately I don't think I can get CPC's out as that was what my instinct said to do as well.
 
Firstly what a great bunch you are - didn't expect replies within 10 mins! Thanks all.
I've just found a USB charging socket that I missed and a bathroom mirror that looked innocent but turns out to have lights and a bluetooth speaker in it with a FCU behind it.
I've had to pack up for the night now but will be back tomorrow.
Thanks again.
 
Think I've found it. Single socket behind sofa with a surge protected extension lead in. Really should have noticed that but customer had assured me there were only two sockets in the lounge. She was quite excited to find this one!
Thanks again.
 

Reply to Interpreting IR test in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
291
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
800
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
831

Similar threads

  • Question
https://professional-electrician.com/technical/replacing-a-consumer-unit-in-a-dwelling-niceic/ All circuits should be tested
Replies
3
Views
1K
  • Question
When you did the further testing and got the 0.06 reading were the CPC's back in the consumer unit? Really when testing you should leave the...
Replies
8
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top