IP 65/IP44 | on ElectriciansForums

Discuss IP 65/IP44 in the UK Electrical Forum area at ElectriciansForums.net

Joined
Jun 12, 2024
Messages
7
Reaction score
0
Location
Stoke on Trent
Main switch room as ingress of dust , the switch room also has many openings to allow the ingress of dust. A recent EICR as coded the Distribution equipment in the room C2 not fit for external influences . One side of the room as an 800A BS 5709 isolator supplying a busbar with 10 BS 5709 isolators supplying various pieces of equipment. Can’t find a decent IP65 MCCB board. Or could holes be sealed in the switch room to minimise the ingress of dust (they should have be done to prevent the spread of fire) and an IP44 MCCB DB used.
 
As we know, dust can get anywhere.
However, it would be unusual to code it c2 for dust penetration unless there is a lot of it possibly from a production process.
A lot more info is needed.

Can the room be sealed off better so there is not a large dust accumulation in there?
 
James thanks firstly for the response. Yes the switch room can be sealed off better as several swa cables enter from the production area into the switch room . I’ve just started working there then they tell me they need to satisfy All C2 on the report for their insurance. I’ve managed to source IP65 protek DBs and can fit smaller MCCB panels in enclosures for other areas of the site but with the one required in the main switch room would be quite big. So in that area I was wandering if I could Fit an IP44 board and seal the room and even put a maintenance schedule in place to clean it any future ingress after that. In order to eliminate the C2
 
Do you mean BS5419?
Seal the switchroom. Is this dust from some kind of production?
Do you mean BS5419?
Seal the switchroom. Is this dust from some kind of production?
Yes BS 5419 must of had a blonde moment when I put the other BS number. The switch room is built adjacent to a production area where swa cables pass through a wall into the switch room . Would you seal all holes first that monitor the switch room for ingress of dust for a few days …. Then if it’s minimum amount of ingress fit an IP44board??
 
Why not just seal the room and clean the existing switchgear?

Is there something wrong with the existing switchgear that requires it to be replaced?
The existing switchgear is to BS 5419 with some of the switches containing asbestos arc shields, also some of the SWA cables are not correctly glanded of properly. Some have BS 88 fuses others BS3036. Also in the event of a fault all three poles won’t be disconnected.
 
What do you mean by 'all 3 poles won't be disconnected'?
Total isolation of a machine is required, where ever, in general locally.
In distribution boards, I've had situations where changing 3036's to 88's removes the asbestos problem. May be different with the switchgear.
 
The fuses aren't linked so if a fault occurs one one phase only then the other two phases will remain live. Whereas with a circuit breaker all phases will be disconnected.
Yes, but does that mean 3 phase supplies via fuses are a no no, though?
I still install them.
 
I don’t think management would like an electrical shut down for 2 or 3 days to change the switchgear… plus extra cost in removing the asbestos….

As suggested, remove the external influences.
 
If you do have to upgrade the switchgear, an alternative solution is to house the whole setup inside an enclosure.

This is pretty commonplace in industrial situations where everything is housed in the one panel.

Obviously each cable will need glanding or similar through the enclosure (just stuffing glands) then finally proper glanding/terminating into each item of switchgear as appropriate.

Depending upon who has access, you can actually use "downgraded" ip kit within this enclosure.

Obviously, only the thing to do if you absolutely need to replace most everything, if it's just a couple of things, just get a higher ip rated unit, or enclose each one individually.
 
If you do have to upgrade the switchgear, an alternative solution is to house the whole setup inside an enclosure.

This is pretty commonplace in industrial situations where everything is housed in the one panel.

Obviously each cable will need glanding or similar through the enclosure (just stuffing glands) then finally proper glanding/terminating into each item of switchgear as appropriate.

Depending upon who has access, you can actually use "downgraded" ip kit within this enclosure.

Obviously, only the thing to do if you absolutely need to replace most everything, if it's just a couple of things, just get a higher ip rated unit, or enclose each one individually.
A 10Way TPN MCCB Distribution Board is qùite large ….. would be difficult to put in an enclosure….however I have seen the gear tray /pan removed from a distribution board & fitted in a stainless steel enclosure in a food manufacturing process area. Not sure if that complies with BS 7671 though???
 
A 10Way TPN MCCB Distribution Board is qùite large ….. would be difficult to put in an enclosure….

As long as the enclosure is big enough it will be fine, enclosures are readily available in that kind of size and much larger.
however I have seen the gear tray /pan removed from a distribution board & fitted in a stainless steel enclosure in a food manufacturing process area.

You can buy the pan assemblies separately for building custom units like that, no need to remove it from a standard DB.
Not sure if that complies with BS 7671 though???

Yes it complies as long as it has been built to and certified to the correct standards, which any switchgear manufacturer should be doing.

Custom switchgear like that is pretty standard for medium to large installs.
 
As long as the enclosure is big enough it will be fine, enclosures are readily available in that kind of size and much larger.


You can buy the pan assemblies separately for building custom units like that, no need to remove it from a standard DB.


Yes it complies as long as it has been built to and certified to the correct standards, which any switchgear manufacturer should be doing.

Custom switchgear like that is pretty standard for medium to large installs.
Thanks for the information much appreciated
 

Reply to IP 65/IP44 in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

E
Welcome @Geraldine you may be better off starting a new thread with more detail as Edd is no longer a forum member.
Replies
60
Views
80K
S
The old cut and paste is a wonderful tool ........................ many a project I've managed to develop SoW with it
Replies
1
Views
7K
S
31. When determining design current, the correction factor that is applied to a BS3036 rewirable fuse is a. 0.752 b. 0.527 c. 0.725 d. 1.725 32...
Replies
1
Views
2K
sxsparky
S
G
Replies
12
Views
32K
moospark
M
F
Replies
1
Views
5K
richy8ball
R

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks