Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss IP rated cu 18th edition ? in the UK Electrical Forum area at ElectriciansForums.net
Needs to be metal, MCG make a very decent compliant IP metal 'garage' DB enclosure.
(edited)
I do not have the BBB to hand, can you quote the regulation? Without checking I was under the impression the regulation concerned does not make any distinction to allow for 'combustible' DB's to be used in outbuildings of residential properties. Happy to stand corrected if I'm wrong.If the shed is detached from the main domestic premises the sub consumer unit does not need to be constructed from a fire rated material and can therefore be plastic?
I do not have the BBB to hand, can you quote the regulation? Without checking I was under the impression the regulation concerned does not make any distinction to allow for 'combustible' DB's to be used in outbuildings of residential properties. Happy to stand corrected if I'm wrong.
This is the reg:
421 .1.201
Within domestic (household) premises, consumer units and similar switchgear assemblies shall comply with BS EN 61439-3 and shall
(i) have their enclosure manufactured from non-combustible material, or
(ii) be enclosed in a cabinet or enclosure constructed of non-combustible material and complying with Regulation 132.12.
NOTE:
Ferrous metal, e.g. steel, is deemed to be an example of a non-combustible material.
And this is from OSG:
Where a consumer unit assembly is installed in domestic (household) premises,
domestic garages and outbuildings, one of the following applies:
..,. the enclosure is to be manufactured from non-combustible material; or
..,. the consumer unit is enclosed in a cabinet constructed from non-combustible
material.
That's cleared that up, right? No. It then goes on to say...
Where the consumer unit is to be located in an external non-habitable building, e.g. a
garage or shed, which is not in close proximity to a dwelling, consideration could still be
given to installing a consumer unit of non-ferrous construction. The term "not in close
proximity" is always a moot point and the decision to install a non-ferrous enclosure
must be supported by a documented risk assessment, which must be appended to the
Electrical Installation Certificate.
Needs to be metal, MCG make a very decent compliant IP metal 'garage' DB enclosure.
(edited)
When you find your BBB can you quote the reg that says a domestic CU must or should be metal. E.G. metal doesn't mean must be or should be and is a mere example of a non combustible materialI do not have the BBB to hand, can you quote the regulation? Without checking I was under the impression the regulation concerned does not make any distinction to allow for 'combustible' DB's to be used in outbuildings of residential properties. Happy to stand corrected if I'm wrong.
I wont look for or find the reg because as you well know it doesn't exist, I used the term metal when I should have used non combustible, so thankyou for correcting that.When you find your BBB can you quote the reg that says a domestic CU must or should be metal. E.G. metal doesn't mean must be or should be and is a mere example of a non combustible material
I tend to steer well away from BG, but having used 2 of these I was impressed by them and would recommend them.I’m installing a sub main in a shed which is brand new but not insulated/ possibility of getting damp.
can I use plastic IP rated consumer unit Or does it have to be metal to be up to 18th edition standard ?
Reply to IP rated cu 18th edition ? in the UK Electrical Forum area at ElectriciansForums.net