Hi all,
I'm planning on adding some lighting to an old stone shed, there's currently a 2.5mm² SWA supply to the shed only supplying one IP rated socket, its fed from a 13A FCU on a 20A radial circuit. This is RCD protected, and the house has a TT earthing system. The run from house to shed is only 5-10m.

Main thing I'm looking for advice on is what brands of IP switches are people using? Or what brands do you like/don't like. Also what IP rated LED battens are good? Heard lots of mixed reviews on both so your opinions will be valuable!

Other question is, is there any reason to fuse down to 3A for the lights, from the OSG 1mm² cable can take 13A in conduit, so would be fine just on the 13A fcu inside, obviously it's easy to add a 3A one in the shed but no point overcomplicating if it's not required? I suppose some light fittings may require <13A fuse so maybe best to add it in anyway??

If you're wondering, my reasoning for wanting IP rated gear with conduit in the shed is because the walls are very crumbly old stone so don't want loads of bits falling off into switches/sockets.

Thanks for any advice!
 
All IP switches are much the same IMHO.

Although there are price differences between say MK and screwfix BG ones, I haven’t had an issue with the cheaper ones yet.

Just make sure they’re not screwed so tight to an uneven brick wall that it distorts the shape, makes it difficult to get the cover on properly.
 
Sorry for the late reply, the shed is physically around 3-4 metres from the closest house wall, and I'd estimate the cable run is 10m maximum. It is actually technically attached to the main house via a neighbours wall and then a garden wall, so I would have thought it can be considered part of the house.
 
BG are cheap and cheerful, but poor quality and the Closing brackets will break after some hot/cold weather. I’ve used Hager a few times and are good quality but stupidly priced. Click also have good ip rated sockets and switches at a decent price.
 

Reply to IP rated switches for shed in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
358
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
910
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Given that, it probably makes sense to TT the shed, unless you can be sure it doesn't act as an extraneous-conductive-part. (The SWA won't have...
Replies
10
Views
718
The 3A fuse is there to protect the current lighting. For additional power you connect from the non protected 3A fuse side.
Replies
1
Views
557

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top