IP ratings on 3 phase distribution board | on ElectriciansForums

Discuss IP ratings on 3 phase distribution board in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

M

msec

Hello all,

I've just carried out the remedial works from a EICR on a small industrial unit ( I didn't carry out the EICR). The 3 phase board had tails entering through seperate holes on the bottom, which was coded as a 2 due to possible eddy currents. I remedied this by cutting out the gap between two of the holes and feeding all the tails through the bigger hole, to which I fitted a grommet strip. I installed blind bushes and locknuts in the two remaining holes.

Based on the advice of an 'electrician relative', the manager has now questioned the suitablity of the new hole, saying it does not comply. My understanding is the top & sides of the board must be IP 4X (not be able to be penetrated by an item 1mm wide and 100mm long) and IP 2X on the underside (that you must not be able to penetrate with your finger, which you can't, not even a small amount).

Can anyone please point me to the relevant regs regarding this, as I seem to be struggling to find anything clear.

Thanks​
 
As far as I was aware it is IP4X for the top horizontal surface, and IP2X everywhere else.

I will look up the reg in a mo.

Reg. 416.2 (BGB)

BTW you could have left the cables in their respective holes, and just cut a slot between the centre hole and each end hole.
 
Last edited:
It is a distribution & storage base for clothes. Originally, there were four holes, looking left to right, neutral & earth through first hole, then L1, L2, & L3 all through other seperate holes.
 
Last edited by a moderator:
ok i was only asking because if it had of been a pemises like a sawmill for example then you would have to consider a different ip rating for the distribution board. i reckon youre pretty close with your understanding of the ip codes but youve got them back to front. ip2x cannot be penetrated a finger or similar 12.5mm in diameter. ip4x is more strict and cant be penetrated by an object (typically wire) more than 1mm in diameter
 
spinlondon, all holes had 20mm brass bushes & steel locknuts so not an option. I'm happy now I have the relevant regs & info, thanks for the replies guys.
 

Reply to IP ratings on 3 phase distribution board in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
344
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
882
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Sooo the client has accepted that we don't want to be fraudulently taking electricity so that worry is out of the picture. But now basically the...
Replies
32
Views
5K
All of the information for MG stuff is freely available from Schneider
Replies
8
Views
767
davesparks
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top