We might need to have a small 3-phase DB in an industrial location that might be exposed to the elements occasionally, though normally it will be covered if rain, etc, is happening. Total current is no more than 32A but I am struggling to find any sort of conventional TPN board that is rated for this sort of thing. Currently I am pondering on making my own using these:
And matching Acti 9 MCB/RCBO but I wondered if anyone on here has a better suggestion?
 
Funnily enough it's nearly identical to the one you posted, but does call itself a 3 phase board even though it's still a kit of parts!
I saw that and its description but I didn't see any matching busbar for it and felt I ought to try and use matching parts if possible, if for no other reason that next inspection it does not get flagged up.
 
Hager do a range that is a skeleton board in an Ip65 enclosure, I use them a lot for farm work
Here is an example.

They are available in GRP and metal!
Sy
 
Hager do a range that is a skeleton board in an Ip65 enclosure, I use them a lot for farm work
Thanks, that appears a better choice for me as other TPN stuff is all Hager. For some reason I never clocked it while looking through the catalogue, but on checking it is there right in front of me!

Oddly though it says "(Not suitable for outdoor use)" but I'm not sure why given IP65, maybe the obvious aspect if door is opened then rating plummets?
 
Thanks, that appears a better choice for me as other TPN stuff is all Hager. For some reason I never clocked it while looking through the catalogue, but on checking it is there right in front of me!

Oddly though it says "(Not suitable for outdoor use)" but I'm not sure why given IP65, maybe the obvious aspect if door is opened then rating plummets?
Mmm that is odd they say that as they definitely are very good at keeping moisture and dust out! (Have silicone will travel!)
Not installed one outside but I have in dairy rooms where they get blasted with water on the wash down!
They do a plastic single phase version as well that I use a lot and that's excellent too, I wonder if that says the same. Again not that I have installed one outside but in a lot of small Barns and stores!
 
Mmm that is odd they say that as they definitely are very good at keeping moisture and dust out! (Have silicone will travel!)
Not installed one outside but I have in dairy rooms where they get blasted with water on the wash down!
Well this location sure will be dryer than that!

Under all normal circumstances this will be dry, but during construction or if something goes badly wrong it might be exposed to rain. I suspect some sealant as you suggest will be enough to make sure things like fixing screws, etc, are all water tight. If necessary I will put a couple of small drain holes in to the base.

Spiders will still get in, but only really small ones!
 
For the fixing holes I use rubber backed washers from roof cladding screws with a dab of silicone on the back just to be sure!
I have installed quite a few of the metal ones over the years and do go back to several every 3 years or so for inspections, a couple of the older ones about 10 years or so are just starting to rust where they have had the coating caught and damaged!
Typical Hager design and build, bulletproof!
 

I've used 'their' IP GRP enclosures before with absolutely zero complaints.
 
I guess that is the obvious solution, have a water resistant box and put a normal DB inside it.
Just use a DIN enclosure and your own choice of CPD, forget about a box inside a box.
 

Reply to IP55 or IP65 (or better) rated TPN board in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
305
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
825
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
912

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top