Hi,
Hope someone can help.

I need to test the prospective fault current at a garage distribution board (i.e. a sub board) but the no trip function of my tester will not work and trips the RCD which serves the garage circuit in the main board.

As I understand it, the figure to take for prospective fault current is the highest out of Ipfc and Ipsc.

So if the highest at the main board happens to be Ipfc then I can easily calculate Ipfc at the garage board by adding R1+R2 of the distribution circuit to the Z given by the meter when testing Ipfc (not sure what this is called but it's like Ze but with the main bonding conductors connected!) then dividing it into 230.

Here's the question:
If the highest figure at the main board happens to be Ipsc then should I be calculating the Ipsc at the garage board using R1+Rn of the distribution circuit rather than R1+R2?

Any clues would be greatly appreciated.
Thanks
 
measure R1 + R2 at the sub board and calculete in ohms and convert to amps and subtract from pfc at source, as a point pfc is not required at db`s if the protective devices ka are equal or higher than the sorce cb`s or fuses as long as the source cb/ fuses can withstand the fault current
 
Surely Ipsc is the maximum current that can flow as the result of a L-N fault so it's the L+ N impedance that's important not the R1+ R2
??
 
Hi,
Hope someone can help.

I need to test the prospective fault current at a garage distribution board (i.e. a sub board) but the no trip function of my tester will not work and trips the RCD which serves the garage circuit in the main board.

As I understand it, the figure to take for prospective fault current is the highest out of Ipfc and Ipsc.

So if the highest at the main board happens to be Ipfc then I can easily calculate Ipfc at the garage board by adding R1+R2 of the distribution circuit to the Z given by the meter when testing Ipfc (not sure what this is called but it's like Ze but with the main bonding conductors connected!) then dividing it into 230.

Here's the question:
If the highest figure at the main board happens to be Ipsc then should I be calculating the Ipsc at the garage board using R1+Rn of the distribution circuit rather than R1+R2?

Any clues would be greatly appreciated.
Thanks

PEFC and PSSC may be measured and then calculated in the way you describe, is this a single phase system?

You need to obtain your Ze(PEFC) at the origin and your Zl(PSSC). Then you need to measure the resistance upto the required point, this will include all live conductors and and circuit protective conductors. Then you can add the resistance of the live loop(Zl) for PSSC and the earth loop(Zs) for your PEFC.

Once you have your resistance then you can calculate your fault current.

If the circuits are greater than 100 amp or utilizing steel armour(PEFC) you may need to consider reactance.

Regards Chris
 
Yes, this is single phase & <100A.

Thanks very much, this confirms what I thought - I couldn't find a proper explanation in any of my books on testing and inspection.
 

Reply to Ipsc and Ipfc at sub distribution board in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
307
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
828
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
929

Similar threads

Regarding the EV, it’s an Ohme charger which I believe has a type A RCD built in, setup would be: 50A RCBO to feed garage db Garage db has no...
2
Replies
17
Views
791
Seen this where T&E has been fixed with a flat bend of too tight a radius.
2 3
Replies
35
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top