Hi,
Hope someone can help.
I need to test the prospective fault current at a garage distribution board (i.e. a sub board) but the no trip function of my tester will not work and trips the RCD which serves the garage circuit in the main board.
As I understand it, the figure to take for prospective fault current is the highest out of Ipfc and Ipsc.
So if the highest at the main board happens to be Ipfc then I can easily calculate Ipfc at the garage board by adding R1+R2 of the distribution circuit to the Z given by the meter when testing Ipfc (not sure what this is called but it's like Ze but with the main bonding conductors connected!) then dividing it into 230.
Here's the question:
If the highest figure at the main board happens to be Ipsc then should I be calculating the Ipsc at the garage board using R1+Rn of the distribution circuit rather than R1+R2?
Any clues would be greatly appreciated.
Thanks
Hope someone can help.
I need to test the prospective fault current at a garage distribution board (i.e. a sub board) but the no trip function of my tester will not work and trips the RCD which serves the garage circuit in the main board.
As I understand it, the figure to take for prospective fault current is the highest out of Ipfc and Ipsc.
So if the highest at the main board happens to be Ipfc then I can easily calculate Ipfc at the garage board by adding R1+R2 of the distribution circuit to the Z given by the meter when testing Ipfc (not sure what this is called but it's like Ze but with the main bonding conductors connected!) then dividing it into 230.
Here's the question:
If the highest figure at the main board happens to be Ipsc then should I be calculating the Ipsc at the garage board using R1+Rn of the distribution circuit rather than R1+R2?
Any clues would be greatly appreciated.
Thanks