I reckon the answer's B.
Some of those who answered "A" may have fallen victim of my "clear as mud" question, in which case, sorry about that.:blush5:
Jimmyray got it spot on:
Just had a quick read, and worked out the combined insulation resistances for the separate DBs. I came out with DB1 = 1.5 Mohms, which is above the required 1Mohm minimum acceptable value to satisfy BS7671, but as it is under 2Mohms, would require further investigation. With regards to DB2, I calculated total Insulation Resistance of 0.6Mohms, which is below acceptable value, so doesn't comply to BS7671. Any good?
The main thing is, to meet the requirements of BS7671:
612.3.2 The insulation resistance measured with the test voltages indicated in Table 61 shall be considered satisfactory if the main switchboard and each distribution circuit tested separately, with all its final circuits connected but with current-carrying equipment disconnected, has an insulation resistance not less that the appropriate value given in Table 61:
(From Table 61):
Up to and including 500V ... ; Test voltage (dc): 500V; minimum insulation resistance: 1.0 MΩ
The main bit is the bit in bold red. There is nothing in BS7671 that says, "If your global IR is less than 1MΩ, don't worry about it if all individual circuits are all over 1MΩ." Nor is there in GN3, or the On-Site Guide. If your global IR is less than 1MΩ (with
distribution circuits disconnected, but with all
final circuits connected), then the distribution board concerned does not comply with BS7671.
Now, I'd always believed that, as long as each individual circuit was >1MΩ you were alright. I could imagine a scenario where I measured the global IR of a board, it was a bit low, so I'd have to measure the IR of each individual circuit to see if it complied.
My understanding now tells me that, in the event of being unable to conduct a global IR on a board and having to test circuits individually, I need to use the parallel resistance formula to check whether the board complies or not when they are all connected.
A note from GN3 (p77, Section 3.10.3 (b) which is concerned with
periodic testing):
The inspector will need to measure the values of insulation resistance for a given distribution board and then take a view based on his/her engineering judgement as to whether the results obtained are acceptable. It should be noted that distribution boards with large numbers of final circuits will generally give a lower insulation resistance value than distribution boards with fewer final circuits.
So for a periodic inspection and test you have a little more "wiggle room". For initial verification: not so much.
Is the above correct? And if so, was it just me who's had it wrong all this time?