just wondering if anyone could help me understand these results that i am testing in my own property on a lighting circuit with all loads removed.
N/E 97.8M
L/E 92.6M
L/N 4.42M

Any help would be great thanks
 
how old is the installation they could be genuine results not everything good will be of the scale
a while ago i put a pic on here of a brand new es lampholder with the lamp out and disconnected it had low readings across all 3 will see if i can find it
 
well theyre acceptable readings, record and move on.

lower l/n could indicate something still attached or slight problem with cabling somewhere, the real issue starts when its below required value and you have to trace it out.
 
Last edited by a moderator:
Strange world ir testing, best of not to dwell on it unless readings are lower than minimum requirements or it's causing problems within the installation unless of course you have the time to rip the place apart :)
 
sorry, missed the " lighting" bit. could just be slight dampness in walls around switches.
 
trying to break the circuit down for some practice but when i connect L/N at one end and IR test from the other end of cable i get a dead short.
thank's for all your help
 
If you've connected L/N at one end and then IR test between L & N at the other end, a dead short is what you'd expect!

If you want to break the circuit down you need to open up the light fittings, disconnect the loop in / loop out and leave them open circuit so you can IR test each leg of the cable.

You might find that each leg of cable is fine, and the problem is with one of the fittings.
 
Do you have two way switches anywhere?
Have you tried the IR test with the 2 way switches in different positions?
Have you tried switching the MCBs off for other lighting circuits?
Is it possible that what you have is a shared neutral?
 

Reply to IR results in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
303
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
818
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
889

Similar threads

  • Question
Thank you for taking the time to help explain this - much appreciated
Replies
7
Views
860
  • Question
It is not that they don't trip, it is that putting a probe in the front of the RCBO to contact the terminal bypasses the sense coil so the RCBO...
Replies
7
Views
675
davesparks
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top