james king
is this test exepatble and does it bypass tranny and bulbs ect? i have been told on here befor ye so i am just wondering
What are you supposed to be testing on your IR .................just a piece of cable, the IR test is not for accessories or luminaires.
I would run the cables, in your conduit or trunking, or whatever your erection method is, do your switch drops and then before I started to fit the luminaires I would do a full IR test on the cable i've installed, and that would mean activating the switches to include the drops. If your switch incorporated a neon, then I would just choc block out the cables and not fit the switch.
This would for me confirm that the cable I've installed is not damaged. Once I fitted all the accessories and luminaries I would do a L/N to E IR test on 250 volt DC just to confirm that i hadn't nipped a cable when fitting the fixtures.
What about if you get a cable trapped, when you put the fitting cover on?
What about if you get a cable trapped, when you put the fitting cover on?
you should also do a P to N test with the switches off.
notihng can be more embaressing as a big bang.
dont be boring Malc LOL
Just noticed after answering this as if it were 2 way strappers ...............
Just noticed after answering this as if it were 2 way strappers ...............
I know i'm going to be shouted out here, you ole idjit and all .......but is there a test method 2 for IR? I know there are 2 methods for continuity of conductors which is Method 1 +2 but I always thought there was just .........IR be it 500v Dc to all conductors, and then there is 250v DC to L/N to E, when did we start calling this method 2 .............have I missed something?