NickD

As per the title really, IR test @250V DC, (L+N)-E, whole-installation test of domestic property, main isolator switch open (obviously), testing caused the piezo igniters on the kitchen gas hob to spark even though no-one was pressing the knob to ignite them, and failure of IR test at about 150kohm. Switching off the appliance FCUs in the kitchen made it stop, IR test then passed at 2.2Mohm. What the hell's going on there?
 
So you’ve shoved 250V DC up an AC appliance and wonder why the readings were strange?

It’s a wonder you’re not buying a new cooker.

Was this an EICR or a specific test on the cooker?
 
Why were you testing with appliances connected?
Why were you testing at 250V?
Why were you testing the whole lot at once?
What results did you get testing between L and N?
How long did you apply the test for?
 
Not sure exactly why it caused the igniter to operate but you're taking a big chance IR testing with appliances of any kind still connected. You're lucky the control board and the ignition board is still working TBH.
 
Not sure exactly why it caused the igniter to operate but you're taking a big chance IR testing with appliances of any kind still connected. You're lucky the control board and the ignition board is still working TBH.


Tested live & neutral connected together and that connection tested to earth. On circuits previously working fine (i.e. no live - earth reversal) that should not cause a problem, esp at 250 volts.
 
The op says he's linked L-N and tested to earth I was told to do this by lecturers and Nic said its ok to do it as a global IR on an Eicr
Personally I'll do it on individual circuits this way on an Eicr just in case something is still connected as a way of highlighting any items still connected before I do the 500v test if that makes sense.
 
The op says he's linked L-N and tested to earth I was told to do this by lecturers and Nic said its ok to do it as a global IR on an Eicr
Personally I'll do it on individual circuits this way on an Eicr just in case something is still connected as a way of highlighting any items still connected before I do the 500v test if that makes sense.

Well that's it the gospel has spoken.

Have you thought what if you have equipment that leaks to earth (eg PCs etc) is still connected your test results could be flawed?
 
Yes I know what your saying and you are correct they should say something to that effect when recommending this method.
But in my experience usually any item such as a pc is connected to the ring in a visible place and you'd be pretty daft not to check the obvious things that may be connected, I did say it was "just in case there are items still connected"
And no I don't believe everything the Niceic tell me but I listed them amongst persons more qualified than me who have given this advice out, I reckon the op got this method from a similar source
 

Reply to IR test sets off gas hob igniters - WTF? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
293
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
802
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
834

Similar threads

Check the clearance between the back panel and/or terminal cover that you've removed. Look for small burn marks.
Replies
3
Views
481

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top